    Can I use a 35/3 mfd 440v dual run cap in place of a 35/3 mfd 370v?
    The dual run cap on my central a/c condensing unit went bad (had a hole in the side of it, leaking). It was a 35/3 mfd 370v dual run. I ordered one on eBay http://cgi.ebay.com/ws/eBayISAPI.dll...=STRK:MEWNX:IT, and I have installed it. The contacter is working, and if I flip the outside breaker on, the unit will cut on (fan and compressor) and will run for 5 seconds and cut off. I shut off the breaker, waited 5 min, and did it again, same result.

    I then looked more closely at the cap and saw that it is actually a 470v. I didn't think that would matter, but would that be my problem? Or just a bad cap? Or did something else happen at the same time that the cap exploded. A/C was working fine, one day it wasn't, found the fan and comp not running, but very hot, found the bad cap. Thanks in advance for your help.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Sep 24, 2010, 04:00 PM

    Curious to hear opinions on this. I have used 470v in place of 370v in emergencies and never had a problem, or course I have always ordered the correct cap and changed it out, so I wouldn't know about long term. Anybody have some info on this. I don't think its going to hurt anything as long as your system is a 240v system. Now if the system where a 440v commercial system, you wouldn't want to use a 370 in place of a 470. Im thinking the 370 or 470 is just the max load you can put to the cap.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Sep 24, 2010, 04:58 PM

    Maybe a bad Cap? Do you have a Capacitance Meter or a Analog Volt Meter?
    Verify the Correct cappacitance is connected to the correct wires.
    gdwrnch29's Avatar
    gdwrnch29 Posts: 2, Reputation: 1
    New Member
     
    #4

    Sep 24, 2010, 05:41 PM
    All seems to be working now. I'm guessing that being that the thermostat was calling for cooling, and I simply installed the cap and then flipped the breaker, that the cap had no charge stored, thus causing my problem? I simply left the thermostat in cooling and the breaker on. Went back out an hour later and she's running, don't know for how long.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #5

    Sep 25, 2010, 12:10 PM

    Glad its working.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

450 mfd capacitor replaced by a 370 mfd [ 4 Answers ]

I don't very much about capacitors but I have a supplier that insists that a 40 mfd 370 VAC rated running capacitor can adequately replace a 40 mfd 450 VAC rated one. Based on what I read, a starting capacitor can vary by up to 10% but that running capacitors must be matched perfectly.

I have a Clarendon Stand up wooden piano mfd by Haddorff Piano Co. [ 0 Answers ]

By the serial number it says it was made around 1910. I am looking to sell it, but no nothing about pianos. Could anyone help me and telling me about how much it would go for or how much it is worth? THANK YOU!

Replaced condenser fan, dual cap, contactor and still... [ 4 Answers ]

Here's the scenerio... Yesterday afternoon, my condenser fan stopped running, but I could hear my compressor running and the relief valve was hissing. Made a trip to my favorite supply warehouse, picked up a new fan motor and dual cap. Installed them and nothing. Well, the compressor...

Run cap and Start cap values for GE 5KCP39KG 5177AS [ 11 Answers ]

Hi there, I am trying to fix an old Goettl gas pack unit. It worked fine till 2 weeks ago. Now it starts normally with colder air for like 4-5 minutes then it sends inside warm air , no cooling . From outside I can see the condenser fan blade starting to rotate for those 4-5 minutes , low RPM...


View more questions Search