    Isolating ground and neutral
    I installed a new conventional residential 200 amp service today. The service is in the house with an external main shut off (breaker) outside, as well as the main breaker at the service panel inside. I was told that I need to isolate the neutral and ground bars, which apparently (though it wasn't explained to me at the time) is because there is a remote shutoff ahead of the main panel. My question is; why would this make a difference? In other words, if I am understanding this correctly, if the feed from the meter went directly to the main breaker in the service panel, the neutral bar and ground bar would be common, or tied together. But isolated if as above. Appreciate it if I knew why. Thanks!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Sep 22, 2010, 04:10 AM

    First off, who was supposed to explain this to you. This is something you should know before going at a big job like this. Codes are important.

    It matters because the neutral conductors are current carrying. This means there is current (NOT voltage) on them any time there is a load. This is why an open neutral causes a circuit to no longer work. Thing is of this happens then the current is looking to go back to it's source. If this were tied together with the grounds then it is possible that the grounding conductors and metal parts would be carrying this current back to the source.
    At the main panel/disconnect there is only one path back to the source, the service cable, which as we know is designed to carry current.

    Forget that the bars are connected in the main. It's what happens to them, and their function after that that matters.
    durban1's Avatar
    durban1 Posts: 3, Reputation: 1
    New Member
     
    #3

    Sep 22, 2010, 06:59 AM
    Comment on stanfortyman's post
    My contractor installed panel has the neutral and ground tied together. Can your above scenario not happen there?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Sep 24, 2010, 04:02 AM

    First off, don't reply by using the "agree/disagree" ratings. That is for a different purpose. For those that care about it getting a "disagree" rating lowers their reputation number.


    Second, I have no idea what you mean with your last question.
    If the electrician installed a main disconnect outside you MUST keep the grounds and neutrals separate on any panels downstream of that disconnect.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Isolating ground and neutral in a subpanel [ 1 Answers ]

Why do I need to isolate the ground and neutral in a subpanel when it is already bonded back at the main panel?

Bonding of the neutral and ground [ 2 Answers ]

I currently have a subpanel coming from a main distro panel with my local power source being a Y connected generator. How many places/panels should the grounded and grounding conductors be bonded? I believe it is the first means of disconnect which is my MDP. All subpanels from that point on...

Neutral / Ground [ 3 Answers ]

OK Strat, Here is the photo clip of the schematic of the Neutral /Grounding system in my place. Don

Open ground when neutral not touching ground [ 3 Answers ]

Hi, I was moving around a room and noticed my wife wanted her desk elsewhere. I decided to, since she would have her computer on it, check the outlet she would be moving to. It seemed old so I changed it. I noticed before I changed it that with my GFCI tester, all sockets on this circuit were...

Using Neutral as a Ground ? [ 3 Answers ]

In my new apartment there are some wall outlets that are two prong outlets. Also my fear is that the three prong outlets are not “physically” connected to ground. I heard somewhere that in this kind of system the neutral wire can also be used as a ground. Is this correct? Would a separate...


View more questions Search