    Maximum vertical head between p trap and drain standpipe
    I'm doing a kitchen remodeling project. I now have a deeper sink basin with a garbage disposal on my double sink, which means I have to lower the p trap by about 6" compared to the previous installation to. My question is.... "What is the maximum permissible vertical (head) separation between the standpipe and the p trap ?"
    - The standpipe vertical height above the floor is about 20"
    - The disposal discharge height is about 2" above the standpipe
    - The bottom of the p-trap is roughly 10" below the standpipe and 3" above the floor of the cabinet, and drains both sinks.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Sep 17, 2010, 07:14 AM
    Quote Originally Posted by ;
    The bottom of the p-trap is roughly 10" below the standpipe and 3" above the floor of the cabinet
    Sorry! But your going to hafta pay for those deeper tubs. You can't make water run uphill.
    The wall will have top be opened up to the vent stack and the sanitary tee and sink arm lowered to pick up the trap. Either that or go back to your old sink. Good luck, Tom
    Barock's Avatar
    Barock Posts: 2, Reputation: 1
    New Member
     
    #3

    Sep 17, 2010, 07:33 AM
    Tom,
    Discharge from the disposal is 2" above the standpipe, so both sinks and disposal should drain. Are you saying that I need more than 2" vertical separation?

    Tim

    Sorry,

    I may have confused terminology. Got it all back together and it works fine. Thanks for your comment.

    Tim
    BuzzBuzzard's Avatar
    BuzzBuzzard Posts: 1, Reputation: 1
    New Member
     
    #4

    Oct 13, 2010, 08:46 PM
    Hi:

    I just went through a similar issue. I installed a new 10" deep sink vs: my old 7" sink. Also, I have an undermount now which makes my new sink 11 1/4" from the top of the counter top. Anyhow, the drain line coming out of the wall is somewhat too high so when I set up my new garbage disposal, I had to reverse my P trap to make up for the high difference. It works great and yes, the water has to go up hill a few inches, but there is no issues. It workd perfectly.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #5

    Oct 14, 2010, 05:02 AM

    We thank you both for the updates. Happy you found your own solutions. If we can ever help in the future just ask. Good luck, Tom

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Maximum horizontal run for drain line before reaching p-trap [ 5 Answers ]

Hello, I want to install a sink in a gazebo on my deck. The 2" drain line will run straight down from the sink then turn 90 deg and run horizontally (sloped 1/2" per ft) into my crawlspace about 15 ft away. The p-trap and vent line (AAV) I want to locate in my crawlspace so it doesn't freeze. ...

Maximum vertical fall distance shower drain to p-trap below it. [ 1 Answers ]

What is the maximum vertical fall distance between the shower drain and the 2 inch trap just below it? :)

Maximum distance from sink to p trap [ 5 Answers ]

Hi, What should the maximum distance be from the bottom of the sink to the p trap. If I stay within this distance is there any problem installing a p trap below floor level? I want to do this because of space limitations when installing a pedestal type sink. Thanks, Tom