    I want to run 200amp service 720'
    I want to run 200 amp service 720' how much would I loose at that distance and a suggested wire size for a 1300sq ft home if it can be done as a secondary line?Im being told a couple of different things!thanks
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Sep 15, 2010, 05:42 PM

    Only have a minute, and can't give you size now, But that Is a Long run, and will be a several sizes larger for sure.
    Cheaper is to have power company run high voltage and poles, and Transformer.
    May be cheaper?
    Underground would be nice(no poles).
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Sep 15, 2010, 06:37 PM

    No way you are going to do this easily, cheaply or even successfully.

    The wire size you will need will be impossible to terminate on typical 200A equipment and lugs. If you go with copper to use smaller wire the price will shock you out of that idea.

    The only logical way is to run primary much closer to the house.
    Your power company will have all the specs you need.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Sep 15, 2010, 06:42 PM
    If you are going to make this a permanent home and pay the power company, they should bring power to it. We are 400 ft. off the road and the power company, an EMC in North Georgia, ran a drop with a transformer to a point 75 ft. from the house. From there, due to terrain in the mountains, they ran another line to an intermediate pole and then 25 ft. to the weatherhead. Cost to me $0
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Sep 15, 2010, 07:14 PM

    Depends on where you are. In my area ALL underground, including primary, is the customer's responsibility.

    Even overhead they will only go like 150' onto customer property, then it is on the customer's dime.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Sep 16, 2010, 02:56 AM
    Stan is correct, many utilities responsibility stop at the property line, and the customer is responsible for extending the power line, no matter low voltage or high voltage.

    When the distance of the line extension is 200 foot or greater, extending the high voltage should always be considered, as extending low voltage any great distance creates a voltage drop issue.

    Mark, you have gotten several answers for wire size because voltage drop calculations are complicated and often misunderstood, require specific details to perform accurate calculations, and often calculations are not done at all or properly, and "rules of thumb" come into play, and all kinds of answers are provided.

    Either you or your electrician need to consult with the utility about extending the high voltage to a point close and reasonable to the home. This may involve several poles or underground high voltage cable, which ever you prefer or are able to afford.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Use a 200amp service panel for 100amp service [ 1 Answers ]

I have a Murray/Siemens LC3040B1200P circuit service panel I would like to use to replace my existing panel. The present service is 100amp and the new panel is 200amp. Is it possible to just change the main to a 100amp main and use the new panel? What is the new main number? Thanks...

How to wire for a 100 amp service to a garage from a 200amp service location [ 1 Answers ]

I have a 400 amp service that is attach to my house and I going to be putting in a garage about 200 hundred feet away from the main service panel, I would like to know what size wire to use for that length.

Got a 200amp service can I run another two 50amp breaker in the 200amp service [ 0 Answers ]

I got a 200amp service put in and I'm trying to get a electric stove in the basement will that 200amp service be enough power for two stove or will I have to run a sub-panel

Change 100AMP service to 200AMP service? [ 2 Answers ]

What are the steps need to change from 100 AMP service to 200AMP service?


View more questions Search