    Transitioning from ungrounded to grounded wire in a 100 year old home with lathe & pl
    I have taken out a wall in an old home with lathe and plaster wall. The existing wire is the old ungrounded wire. I want to transition this wire to a new outlet. It appears that the old wire has been stapled to the studs during installation. Any ideas on how to transition the old wire using 12-2 wire to an outlet?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Aug 5, 2010, 08:06 AM

    My opinion would be to to pull a new home run from the panel and then rewire the entire room, if you are up to that type of work. If you have done 60% or more of renovation to the room, then you are required to bring that room up-to code. NEC 2008 code also requires that you use a AFCI on most rooms no-a-days.

    However, there is an easier way, again depending on the percentage of renovation you are doing. You can replace the existing receptacle with a GFCI receptacle and notate on the new receptacle that there is no equipment ground.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire service, wire gauge 100 amp [ 9 Answers ]

I'm installing a 100 amp service in the backyard with a separate meter on a pole next to sub-suface power tranasformer. I have a 100 amp meter box on one side of the pole and a 100 amp braker panel with a 100 amp main breaker on the other side. I'm going to place in it a 15-20 amp breaker for gfi...

What size wire for 220v 100 amp service at 100 feet [ 7 Answers ]

I am running 220v 100 ft to a 125 amp sub panel. A welder would be the heaviest thing used. (around 200 amp welder) what size copper wire would I need running in pvc underground

Wire UF wire to run to new 100 amp service panel? [ 10 Answers ]

My house has a 200 amp service. I have a new 30x40 building in back. I have a 100amp Square D load center for the building. I want to run a line from the house to power the building. Big items include, air comp 30 amps, welder 50 amps, other raidial arm saw, ban saw pipe saw 15-20 amps? It is...

Can I run a 50 amp subpanel if a 100 amp main if so what size wire [ 1 Answers ]

Can I run a 50 amp subpanel from a 100 amp main and if so what size wire

Replacing an ungrounded outlet with a grounded one [ 11 Answers ]

I would like to replace my 2-prong (ungrounded) outlets with 3-prong (grounded) ones. I didn't see a ground wire when I removed the outlet. How can I replace an ungrounded outlet with a grounded one? Also, how can I find out if my outlet box is grounded?


View more questions Search