Jul 29, 2010, 07:19 AM
|
|
Will a bad Capacator cause a Condenser Fan Motor To get hot?
My Central A/C is starting to blow fuses. The fuses are located in the A/C unit. The fuses blew and when I replaced mthem it took about 9 hours and the fuses both blew again. I replaced them and they blew after about 20 minutes. They are 30 amp time delay fuses. I checked and the fan motor was very hot. Is the Fan Motor bad or is the Capacitor going bad? It is a GE. I don't know the tonnage. Anyone have any solution. I will appreciate any help.
|
|
 |
Uber Member
|
|
Jul 29, 2010, 08:17 AM
|
|
Ye, and if you can't test the capacitor, Replacing is a quick cheap test.
Does the motor spin freely?
|
|
 |
New Member
|
|
Jul 29, 2010, 09:03 AM
|
|
The Fan motor spins very freely. As soon as I replace the fuses it will run perfectly and then blow fuses again. I have a breaker in the main panel, so I cut two pieces of copper pipe and put them where the fuses go. It came on and ran for about 20 minutes and then threw the breaker. I checked the fan motor immediately and it was very hot. It was able to spin very freely. It was just hot. Thank you so very much for your quick reply.
|
|
 |
Uber Member
|
|
Jul 29, 2010, 11:26 AM
|
|
I would try a new cap and test, then install new fuses.
The Fuses did a good job telling you the motor has a problem.
|
|
 |
New Member
|
|
Jul 29, 2010, 11:35 AM
|
|
 Originally Posted by Stratmando
I would try a new cap and test, then install new fuses.
The Fuses did a good job telling you the motor has a problem.
Hey.. Stratmando.. Thanks so very much. I will try new Caps. The Fan Motor was very hot but did not freeze up. That was where I was confused, I just wondered if the Cap would be bad and that was what caused the Fan motor to get hot and blow the fuses. I 'll take your kind advice. I guess if the Cap does not solve the problem, I'll have to spring for a new blower motor?
|
|
 |
Uber Member
|
|
Jul 29, 2010, 11:43 AM
|
|
Only other thing you could do is with power isolated from motor, check each lead to the motor for resistance to ground. Scales of rust can fall and cause problems.
|
|
 |
New Member
|
|
Jul 29, 2010, 12:54 PM
|
|
 Originally Posted by Stratmando
Only other thing you could do is with power isolated from motor, check each lead to the motor for resistance to ground. Scales of rust can fall and cause problems.
Thanks... I'll let you know how this works out. I am a disabled 75 yr old veteran. Just can't afford to call a tech. I appreciate so very much your help.sure is hot here in Fla.
|
|
 |
Uber Member
|
|
Jul 29, 2010, 02:56 PM
|
|
I feel your pain, I may be a little further south, Tavernier.
More info is always here.
Trying capacitor first?
|
|
 |
New Member
|
|
Jul 29, 2010, 05:40 PM
|
|
 Originally Posted by Stratmando
I feel your pain, I may be a little further south, Tavernier.
More info is always here.
Trying capacitor first?
Yes... I'll do the cap thing. And then look for a used Fan Motor if the caps prove not to be bad. Until then I'm putting the window units to work. I tried the test you mentioned but my tester must be on the outs as well. I live in a rural area anjd they want to charge quite a bit to come out this far. I can't blame them though. I'm sure with the help you gave me, I'll be up and running in a few daYS.. tHANKS AGAIN
|
|
 |
Uber Member
|
|
Jul 29, 2010, 05:47 PM
|
|
Good Deal, Good Luck. Let us know the damage. Take Care
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Trane condenser fan motor to A.O.Smith condenser fan motor
[ 2 Answers ]
The Condenser fan motor I removed from a Trane unit had four wires 1 black, 1red, 1brown and . The black wire went directly to #3 on the relay, the red wire went to the capacitor with black wire from #6 on the relay the brown wire went alone to the other side of the capacitor.
I purchased...
Condenser fan motor
[ 1 Answers ]
My condenser fan motor burned out. Does the rpm (825 or 1075 ) of the replacement motor make any diiference if the size (5 5/8),voltage (208-230), are same and amps (1.6-1.9) are in the same range
Condenser fan motor
[ 5 Answers ]
Hi my unit is a Rheem the condenser condenser fan is making a hooming noise like is a turbine not a fan I wounder if the blades or the contactor making that noise the fan that I had was a original from the manifactory but it was stoping went it got to temperature well I replaced it with one that...
Condenser Fan Motor
[ 1 Answers ]
I meant to say where on the contactor does the black and white wires go I already put the browns on the capacitor thanks for all your support
Condenser Fan Motor
[ 1 Answers ]
I have searched th web for a cross-match for a condenser fan motor for a RHEEM model RAKA-036JAS 3.0 Ton A/c Unit To no avail.
R.S. R.Ph.
View more questions
Search
|