    Ac compressor humming
    Our Ac Unit is not cooling and the compressor is making a soft humming noise. The fan is not turning on. At first we thought it was just BGE and their Peak Rewards "regulating" but now we are thinking maybe the AC is broken... any ideas? We have small kids...
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Jul 24, 2010, 07:33 PM

    Humming is a good sign. Don't run the AC until fixed.

    Either the fan or the fan's capacitor has failed. With the power off try to move the outside fan manually. See if it moves freely.

    Capacitor is usually physically inspected for bulges etc and electrically tested. Motor is checked for binding and open windings.

    If motor is replaced, both cap and motor are replaced together.
    MaMaNewman's Avatar
    MaMaNewman Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 24, 2010, 07:41 PM
    The fan does move freely. So I guess we call someone in the am?

    Thanks!
    nugentoffer's Avatar
    nugentoffer Posts: 23, Reputation: 2
    New Member
     
    #4

    Jul 25, 2010, 01:07 PM

    Why do you need to replace the cap and the motor at the same time?

    My motor just went bad yesterday, but only bought a new motor. Cap tested out good at appliance shop..
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #5

    Jul 25, 2010, 01:16 PM

    If the new motor capacitor rating matched the old capacitor, you should be just fine. But its very important that the motor matches the cap. If not, it will shorten the life of your new motor. Capacitors are extremely cheap, so its always cheap insurance to install new matching cap when installing new motor. If you had the old cap tested, and it was rated for you new motor, you are okay.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #6

    Jul 25, 2010, 04:04 PM

    Quote Originally Posted by neugentoffer
    Why do you need to replace the cap and the motor at the same time?
    High value capacitance capacitors have one of the highest failure rates in electronics. The motor usually outlasts them. They degrade.

    Simple capacitor meters are good at guessing whether a cap has failed. Shorts are easy. Capacitance out of tolerance is yet another way. ESR or effective series resistance is a better test. The behavior in a hostile environment where temperature and voltage surges hammer the cap, your pushing the popensity to fail.

    When I rebuild audio stuff or rebuild antique radios, the caps above a certain value, are just replaced. If there is any electrolytic cap in the signal path, it's changed to a metalized polester.

    5 years is a good time to replace. If the cap shorts, it cn take out the motor. Cheap insurance policy to replace the cap when the motor is replaced.
    nugentoffer's Avatar
    nugentoffer Posts: 23, Reputation: 2
    New Member
     
    #7

    Jul 26, 2010, 07:03 PM

    Don't mean to hijack this thread, but how do you know if a capacitor is rated correctly for the motor?

    Is there some sort of marking on the motor that will tell you what type of cap. To use with it?
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #8

    Jul 26, 2010, 07:26 PM
    Quote Originally Posted by nugentoffer View Post
    Don't mean to hijack this thread, but how do you know if a capacitor is rated correctly for the motor?

    Is there some sort of marking on the motor that will tell you what type of cap. to use with it?
    Yes,on all new motors
    There is a label that tell the correct capicitor needed
    It's there where it gives the wiring instructions,the voltage,the rpm`s,
    Most times they even put it on the box the motor came in

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Compressor making a humming sound [ 1 Answers ]

I have a goodman unit that is making a (semi-loud) humming noise. Everything is running but it is not cooling the house. I had a tech come look at, he hooked up his guages to it and both side were reading about the same. He put 2 lbs of r22 in it and it did not change, both guages read 130. He...

Heat pump outdoor fan runs not compressor voltage at compressor good. New compressor [ 1 Answers ]

Have a new compressor. Just replaced fan runs compressor does not, have voltage at the compressor plug? What could stop from coming on high side and low side equal at 100psig.

AC Unit not working. Fan out, compressor making a humming noise. [ 19 Answers ]

So do you guys have any other ideas of what can be causing this issue? - Furnace fan blowing when AC on. - From the AC Unit outside you can hear a hum coming out of the compressor and you can hear a click coming out of it once in awhile. - The Fan of the AC Unit is not moving at all. Is...

New a/c, humming compressor [ 1 Answers ]

Hi, I had a new split central heat/ac unit installed a few days ago. The compressor is making a very loud humming noise. The unit is a goodman (3 ton 13 seer R22). The tech worked a very long time trying to get the unit to cool. (it was cooling just fine, I checked the air temp coming out of the...

Amana air conditioning compressor fan runs but compressor does not [ 9 Answers ]

I have an Amana Model RCE30A2B Compressor unit installed it is about 6 years old, the compressor will not cut in when demanded yet the cooling fan for the unit does


View more questions Search