No Blower in on or auto
I have a package unit outside. The ac stopped working. TStat seems to be working fine.
In the past, I replaced the control board 2 years ago, compressor fan motor 3 years ago along with all 3 capacitors.
There is no fan in fan or auto modes. The squirrel cage spins nicely by hand and checked power, it is there at the motor with the tstat in fan mode, but no spin. Power not flowing through the contactor ( not plunged in).
I replaced the transformer, because that is often the problem with no fan? Replaced the contactor because the resistance was less than 10 ohms between the low voltage sides? No change
The control board has a 5amp fuse which I reseated and checked.
There is no power between R and C. Am I looking at a board change again? Thanks in advance.
|
|
 |
Uber Member
|
|
Jul 21, 2010, 08:26 PM
|
|
If you have voltage to the motor and it doesn't spin, don't mess with transformer, thermostat or anything, the problem is at the motor.
I would suspect Transformer, or fuse if I got NO response ftom thermostat.
Also see if 240 volts is present on line side of contactor, and 240 volts on load side when energized.
|
|
 |
New Member
|
|
Jul 22, 2010, 12:15 PM
|
|
There is power on the line side, but the contactor never energizes.
 Originally Posted by Stratmando
If you have voltage to the motor and it doesn't spin, don't mess with transformer, thermostat or anything, the problem is at the motor.
I would suspect Transformer, or fuse if I got NO response ftom thermostat.
Also see if 240 volts is present on line side of contactor, and 240 volts on load side when energized.
|
|
 |
Heating & Air Conditioning Expert
|
|
Jul 22, 2010, 03:07 PM
|
|
The contactor is energized by a 24 volt signal circuit. Break out the good old voltage meter and start back tracking the circuit to find the problem.
|
|
 |
New Member
|
|
Jul 27, 2010, 04:46 AM
|
|
OK. I started checking power and found that only 1 leg of the double pole contactor was getting power. So I replaced the circuit breaker. Now the Compressor and its fan now work but still no blower motor. I checked power at the blower and it had 110v, 27v, 18v at the com, hi and low connections. I thought that it was the blower that was bad now until I found that it was supposed to be 240v. So I ran a jumper to the fan from the board and the fan powered up. I then took the board off and noticed a big burned arc spot on it. I replaced the board and now all is well.
Thanks
 Originally Posted by hvac1000
The contactor is energized by a 24 volt signal circuit. Break out the good old voltage meter and start back tracking the circuit to find the problem.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
T-start fan on/furnace blower on, AC w/fan on/auto, blower off
[ 8 Answers ]
If no cool or heat, just fan on, there has blower start in furnace;
While in air conditioner, regardless fan on or auto, there will be no indoor blower on at all;
While outside condenser and its fan seems fine.
I lready jump wires G, RC and Y in T-start, won't see any difference.
By the...
AC blower fan will not run in auto, only "ON". (heater runs in auto fine).
[ 2 Answers ]
AC problem. My blower fan will not run in auto. (heater runs in auto fine).
The fan will run in "on" position. I suspect the timer (or maybe a limit switch if there is one) on the fan control board. Does anyone know where I can get a schematic for the Lennox BCC2 fan control board?
Thanks...
Blower will not run in auto
[ 1 Answers ]
My central air and heat air handler blower will only run in the on position. Had been working fine in auto until today? The outside compressor etc. start and run as they should with thermostat setting. Unit is cooling fine just have to keep blower in on position.
Fan Blower will not come on in auto
[ 8 Answers ]
Blower will only come on when in "ON" position. "Auto" position will not cause it to go on. One can hear the thermostat click (basically saying its time to kick in) but the blower will not commence until I manually set it to "ON". At first, I thought it was thermostat so I replaced it with a...
Blower does not work in Auto
[ 1 Answers ]
Ihave an older electric forced air heating system. With the system in heat the blower will not run in the auto mode. The heat does seem to work, it will heat the house. During the airconditioning season it worked fine. During the A/C season I didhave to change a relay. I wired it IAW the...
View more questions
Search
|