    Evaccuating system
    When you get a system in a vacuum @ 500 microns and let it set for over night how much lee way are you allowed on the micron gage up to 600 are more?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jul 20, 2010, 10:50 PM
    Quote Originally Posted by danpatm View Post
    When you get a system in a vaccum @ 500 microns and let it set for over night how much lee way are you allowed on the micron gage up to 600 are more?
    When a system has been evacuated below 500 microns, the pump has been shut off and the micron gauge is connected, if the vacuum rises to 1500 microns and stops, there is moisture remaining in the system. If it rises above 1500 microns AND continues to rise, there is a leak. You should allow at least 15 minutes after the pump has been shut off to have this micron gauge reading be accurate. Most of the time when a system will not evacuate below 1500 microns there either is a lot of water or there is a fairly large leak. Regardless, a micron reading taken when the pump is running is useless unless the micron gauge is attached to a totally different part of the system and not connected in any way to the gauges being used to evacuate the system.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #3

    Jul 21, 2010, 03:21 PM

    If you are saying you pulled to 500 and let set overnight with the pump off, and it only went up to 600, or a little higher, then you should be just fine. When I pull a vac, I pull to at least 250 and let it set for roughly half an hour. If it rises above 800 I re vac and go from there.
    danpatm's Avatar
    danpatm Posts: 28, Reputation: 1
    New Member
     
    #4

    Jul 22, 2010, 04:10 PM
    Comment on mygirlsdad77's post
    When you re vac do you add nitrogen to the system first and then re vac?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #5

    Jul 23, 2010, 03:10 PM

    Not always. If I'm in a hurry, I will purge the system again with nirogen, but if I have another job to go to I just leave the pump run while at the other job. I do however always purge the system with nitrogen before the initial vac. Its really amazing how much quicker it will pull a good vac.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Converting forced hot air system to baseboard heating system [ 2 Answers ]

Hi, I have a basic question about heating. Is it possible to change a forced hot air system to a baseboard heating system? And if so, what does it involve exactly? And approximate prices, for about 5000 sq feet house. Thank you very much.

97 honda passport fuel system too lean mass bad air flow system [ 1 Answers ]

I have a 1997 Honda Passport with the 3.2 V6 which I am trying to fix. The OBD2 is saying the fuel trim system too lean (cylinder bank 1 code # P0171) and the mass air flow system performance problem code#P0101. I am not sure what it is that is wrong. Can someone tell me where to start?

Converting forced hot air system to baseboard heating system [ 1 Answers ]

When considering converting from forced hot air to baseboard heat, is it possible to just add piping / water boiler / baseboards and do nothing with the forced hot air system (use it for AC) ?

Smoke extract system & staircase press. System [ 2 Answers ]

I am working for a 35 storey tower. There are smoke extract and staircase/lift lobby pressurisation system in case of fire. Now consultant has already given the CFM required for these Fans, but I have to submit the calculations for the same to the Local Govt. authority. So please help me if...

How do I increase H2O pressure on well system with a water filtration system? [ 2 Answers ]

Howdy, I would like to know how I can increase my water pressure. My current system uses a well pump with a small pressure tank, and "D" control valve. It then runs through a WATERSOFT filtration tank, RAINSOFT water softner, and on the Hot water side, an AQUASTAR on demand hot water system. I...


View more questions Search