    Condensing unit trips breaker
    I have an approx. 25 year old Rheem condensing unit. There is no visible markings identifying the Model or serial numbers. On occasion, it trips the breaker at the breaker box. I have replaced the breaker, checked all of my connections, and tested my capacitors(date code 86-44). This is all good. This condition does not happen on every start-up, but is getting more frequent. I have done an amp test at start-up. On the times that it does not trip the breaker, it draws 23 amps. On the times when it trips the breaker, it draws 65-72 amps. Locked rotor current is rated at 73 amps. The unit has a 240 volt,2 pole contactor, w/24volt a.c. coil. I can not read any of the data on the contactor. The fan motor is drawing .9 amps, as is the nameplate rating. Any suggestions that you might give would be appreciated. Please give approx. price of any part that you suggest that I try. Thanks, cey146
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jul 7, 2010, 03:36 PM

    The old girl probably could use a hard start kit. As it gets older sometimes they get cranky and need a little boost to start. An after market easy to install unit like a kick start might just work for the situation.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

AC unit outside kicks on for 2 sec. Then breaker trips [ 6 Answers ]

When the thermostat kicks the AC on the unit outside comes on for 2 seconds then trips the breaker. The blower inside the house stays on but because the compressor outside isn’t running it just circulates the warm air. The AC unit is on a 30 amp breaker switch so I believe that is large enough to...

Trane ac electric heat unit trips breaker [ 0 Answers ]

I have a Trane A/C split unit with electric heat. Turn on the heat and it runs for 3-5 minutes then trips the 60 amp breaker. Removed the heat strip and inspected with no visible problems to the coils or connections. Wiring is #10 and looks to be in good shape. Where else can I look to resolve...

Central heating unit trips breaker after twenty minutes [ 1 Answers ]

The central heating unit comes on and heat for about 20 minutes then the breaker trips off if I reset the breaker the unit comes on but there is no heat

Bathroom GFI outlet trips breaker at breaker panel [ 2 Answers ]

Hello all. Our house is approximately 13 years old. Each morning when both the iron and blow dryer is plugged into two separate GFI outlets in the master bathroom, the circuit will trip the 15 amp breaker in the breaker panel. Is it possible to upgrade the breaker to a 20 amp without...

Carrier Outside Unit Trips Breaker [ 9 Answers ]

I have a Carrier Central Air Unit, last night the vents started blowing warm air. The blower in the basement was obviously working so I went outside to find that part of the unit not operating. I went to the breaker in the basement to find it tripped. I turned off the ac unit at the thermostat and...


View more questions Search