    Adding a sub panel with aluminum
    I have 125' Aluminum wire that I want to use add a sub panel to a post or RV. The RV requires a 30amp outlet. Also, I want to add a yard/security light to the subpanel.

    The wire I have is (MT 2 AWG AL XLP 600v 2004)
    I got it from Excel when they borrowed my power to feed the neighbor when they were down.

    Couple questions:

    Does this go into a junction box where I splint into copper wire to run to main box?
    Can this wire be buried in 2" conduit for the 125' from cabin(main box) to sub box?
    Is the sub panel necessary, or can I use a outdoor box with a breaker?

    Any ideas?

    Thanks,

    Joe
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jun 23, 2010, 08:59 AM
    Joe

    Sorry for the delayed response.

    I just did a quick look at the NEC 2008 Code book and was able to find cable type "MTW", which is defined as a Machine Tool wiring in wet locations (60C) or in dry locations (90C). Table 310.13 <Moisture, Heat and oil resistant> wire.

    I cannot determine if this is a cable or single conductor wire. Also I cannot find cable type "MT".

    So here are some questions for you:

    What will the be the load calculation for the sub panel?

    Did do know that a sub-panel feeder is required to be four conductors?

    Are you planning for a service drop (overhead feed) or a service lateral (Underground feed) to this sub-panel?

    Can you provide a picture of the cable for me, please?

    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jun 23, 2010, 02:26 PM
    XLP is a direct buried type of insulation.

    The cable is probably four wire, and is called URD.

    Splicing will need to be in a junction box or a buried hand hole.

    4 Wire #2 URD cable will do better in 3 in PVC, esp if there are sweeps/elbows, that distance, but 2 In with no ells will work.

    If you only need two circuits, a 2 circuit panel rated NEMA 3 R , Raintite, will work.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Adding another panel from a 200 amp service panel [ 3 Answers ]

Hi everyone, this is my first post. I have a 60 x 100 ft shop that has a 200 amp service fed in from the pole. Well I added a living space in the shop, which is about 720 sq ft. I plan on doing all the wiring myself and need a little advice on what kind of panel I should use? The living quarters...

Sub panel bonding/aluminum service drop [ 5 Answers ]

Hi, My post is about sub panel bonding, and the use of an aluminum service drop. First, I'm in the process of installing a sub panel at the far end of my basement for my shop. I've researched various posts on this board, and also referenced the NEC. I know the neutral is only bonded at the...

Max Amps in a Panel and adding a sub panel for more circuits [ 3 Answers ]

Hello all, I recently moved into a condo with a 200 amp panel (in my unit). The main panel is in the electrical room of the building and my unit was previously a commercial retail space. I did some remodeling and my panel is now full. The total combined amps of all the circuit breakers...

Connecting large gauge aluminum wire to service panel [ 2 Answers ]

I've completed a beautifully (inspector approved) installation of a new 200 amp service panel to my home (upgraded from 100 amp). I have now strung a 0/0 underground aluminum cable in sched. 80 conduit from my barn to the main panel to connect a sub-panel in my barn to this new 200 amp panel. ...

Using Aluminum Cable for 100 Sub Panel [ 2 Answers ]

I'm going to be installing a 100A sub panel in my garage and need about 125 feet of cable. The price of aluminum is about 1/3 of copper so I'm just wondering what needs to be done differently when installing aluminum vs copper? Is it worth the hassel and/or risk? Thanks in adance! Pete


View more questions Search