        Single Phase 208?? 
       
      
    
    
    
                  
        Greetings, 
I'm about to purchase a Suspended unit heater for a carpentry shop.  I'd like to use a service I previously used for a table saw, being 208v 30A, (2 hots at 120(120degs opposed) and a ground).  The fixtures I'm looking at, in the catalog, state that they are Single/3 phase 208 or Single phase 208.  My real confusion here is that I have no idea what single phase 208 is since 208 is derived from 2 legs of a true 3 phase system.  Any ideas?   
 
Thanks
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Uber Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Dec 12, 2006, 11:31 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        So I am assuming that you currently have a 3 phase 4 wire 120/208 volt system? 
 
For 208 volt single phase, use a two pole breaker, which can connect to any two of the three legs in a  phase panel, to get 208 volt 1 phase. 
 
If you truly have three phase 208 volt, then I would suggest you get a 3 phase heater. But if your circuit you want to use is only as you say two hots and the ground, then you need a single phase 208 volt heater. 
 
Did this answer your question?
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Dec 12, 2006, 11:38 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        I see, so something listed as "single phase 208v"  is still actually from 2 legs of a 3phase 120v system.   
What is the difference from a single phase 208v and a 3phase 208v if both would ultimately only be using 2 of the hot legs?   
 
And yes, I do have true 3phase in the building, it's just that when we install the table saw, years ago we ran 10/3 to the branch panel and used a 30A double pole, so on the level where the Heater is going is only 2 hots/ground of a 3phase system. 
 
It seems like I just got hung up on a nomenclature thing.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Uber Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Dec 12, 2006, 11:44 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Single phase 208 circuit will use two hot legs, and a three phase circuit needs all three hot legs. 
 
All circuits will need the ground. 
 
If any circuits need 120/208, either 1 phase or 3 phase, then the neutral is needed.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Dec 12, 2006, 11:53 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Okay, that's what I figured (as far as what was meant by 3phase 208v).  I was just unsure of what was meant by the single phase 208v.  Now I know,  thank you much.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Aug 28, 2012, 09:04 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        I need a little clarifictaion on this subject. 
 
If single phase voltage is 120. What is the two phase voltage? Is it 208 V or 240V.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               Uber Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Aug 28, 2012, 09:34 AM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        Two hot legs of a three phase system is still single phase, and would be 208 volts.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
	
	
		
	
	
  
    
    
    
      
                  | 
            
      
              
               New Member 
              
              
              
              
       | 
        | 
      
                
               
                
                  
                      Nov 2, 2012, 04:58 PM
                  
                 
       | 
     
     
    
   | 
 
  
    | 
    
    
       
        
        
        
       
    
    
    
    
                  
        2 phase or polyphase is rarely used, don't even concern yourself with this.
     
     
    
    
    
    
    
    
  
   | 
 
    | 
        
                
      
       
        
         
     | 
 
 
	 
	
		 
	 
 
 
 
 
     
  
   
  
   
  
  
  
  
  
  
  
  
  
  
  
  
  
  
    | Question Tools | 
    Search this Question | 
   
  
    | 
    
    
    
     | 
    
    
    
    
    
     | 
    
   
   
   
    Add your answer here.
    
    
 
Check out some similar questions!
2-phase vs 3-phase degrees of separation
 [ 5 Answers ]
At work we have 3-phase power.  I understand the oscillations are 120 degrees apart. 
 
At home I have 2-phase power.  Are the oscillations 180 degrees apart?  I understand the neutral on a 240v circuit should carry 0 as the phases cancel each other out. 
 
My real question is that if we have a...
 
 
208v single phase wiring
 [ 1 Answers ]
How do I connect a 208v single phase appliance to my home circuit panel?  I installed a 30amp breaker which has 2 connections, red and black (hot), then I have white (neutral), and green for ground.  The device only as 2 connectors not 3, plus ground? 
 
Thanks
 
 
How to view single record of ALL people at single address?
 [ 5 Answers ]
I have a table with addresses and names. I can easily sort it by address to see all the people living at the same address grouped together. However, this is problematic with mail-merges, since I wind up generating a new letter for each person, sending multiple mailings to the same residence. 
...
 
 
120v/208v single phase appliance wiring
 [ 2 Answers ]
Recently purchased a coffee machine that has the above reqts.  I understand that it has 220 and 110v circuits that need power.  I also purchased a generator to power this brewer outside.  If I use a NEMA L14-30P plug, to connect into the generator, What is the sequence of wiring for the plug three...
 
 
 
View more  questions
Search
 
 |