    Wiring double pole breaker for two different srevices. One for my travel trailer
    Wiring a new outlet for my travel trailer. I have a double poled 30 A breaker that I plan to use. Can I use one output for the trailer and the other for additional electrical outlets for outside uses ei: lighting, saws... Will this still provide 30 Amp service to both outlets? If so please explain to connetion process.

    Thanks
    Stik
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jun 15, 2010, 11:20 AM
    Using a 2 pole circuit breaker for two 120 volt circuits is not a problem, however, a 30 amp circuit canot be used for lighting and outlets.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring Hot Tub and using a 50 Amp Double Pole GFCI Circiut Breaker [ 10 Answers ]

:confused: I keep getting the GFCI breaker tripping after wiring my hot tub. I wired 2 hot Red and Black to the proper terminals and the White to the neutral and the Bare Copper to the ground Post at the tub. I am using 6-3 w/G per instructions. Could the GFCI breaker be bad? When I wire...

Wiring single pole thermostat in double pole fixture [ 3 Answers ]

Hello, I am trying to install a line voltage programmable thermostat into a manual thermostat fixture. The programmable thermostat is Honeywell RLV430. Instruction manual here: http://www.homedepot.ca/wcsstore/HomeDepotCanada/images/catalog/b7867367-6c05-4c82-a97c-648044b91564.pdf The...

Breaker panel for travel trailer [ 1 Answers ]

I plan to park a travel trailer on my farm. I will have to put up a meter pole, The power company requires that this pole is no further than 70 feet from the pole that contains the primary power . There will be a additional charge by the power company if the distance exceeds 70 feet. The leads for...

Connecting a Double Pole Breaker [ 1 Answers ]

I have to start a motor by energising a Contactor, and I have only positive 24 volts dc,but the connection needs positive as well as negative 24 vots dc. How can I get Positive,negative 24 volts dc from only positive 24 vols dc..

One pole of untied double-pole circuit breaker breaks [ 5 Answers ]

I recently purchased a new dryer (220 v appliance) to replace an older model. The old dryer was connected to the panel via a double-pole breaker except that there was no clip or tie between the poles. I changed the location of the outlet when installing the new dryer, replacing the cable with the...


View more questions Search