    Want to run four circuits from main to outbuilding
    I have room for four 20 amp breakers in my service panel. I want to run four 20 amp circuits to a detached building 100' away. Can I run four stranded #12 wires with one #12 for ground in poly pipe to the building? Is #12 large enough or will I need # 10? I plan on two lighting circuits, one kitchen circuit with microwave, refrig, no electric stove, Another circuit for freezer. Largest load is microwave at 1200 watts.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jun 15, 2010, 08:09 AM

    Actually, I do not believe that you can run four separate circuits. NEC Code requires that there is only one entry point.

    You would be much better off running a feeder into a sub-panel into the detached building.

    To correctly size the feeder, you will need to do a load calculation for the detached building.

    If your detached building is going to have a kitchen, then you must provide two 20 A circuits. That's required by the 2008 NEC code. Receptacles serving the counter top, must be GFCI protected also.

    Bathroom(s) will require GFCI protected receptacle outlets.

    Might I suggest that you contact three or more licensed electricians to plan and bid this job.
    Chair_Man's Avatar
    Chair_Man Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 15, 2010, 11:08 AM

    Thanks Donf! I can do a subpanel. Believe me, if I could afford a contractor I'd let them do it, but a Rockafella I ain't (these days they probably say: a Warren Buffet I ain't).

    Anyway, what I have gleaned from other posts is: a 60 amp feeder using #6, three conductors one ground with a 60 amp disconnect at subpanel, isolate neutral and ground bus, install a grounding rod for subpanel. I think that 60 Amps is way over kill as this is a 300 square foot cabin, far, far, far, from the maddening crowd. There are no 240v loads and if you turned everything on at the same time, total load would not exceed 3000 watts/25 amps. Could I do a 30 amp subpanel?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Why or when for a main serivce run do you use a neutral or just a ground ? [ 10 Answers ]

So sometimes from the pole, you have your 2 hotts and 1 neutral, however sometimes you have 2 hotts and a ground and no neutral, So here's what I'm doing in a few days, taking a 200 amp panel putting in a 100 amp breaker going underground with it, than poping back up and splicing in a 100 amp...

Can I run two light circuits with one switch? [ 3 Answers ]

I will be installing (10) 6 tube high bay fluor light fixtures in a new shop. Each fixture draws 214 watts for a total of 2140 watts. 2140W / 120V = 17.83A . I know I need 2 circuits, (one 20 amp circuit can safely carry 16 amps). But I would like only one switch to control all the lights. Is it...

Are there restrictions for two circuits sharing one 12/3 at the beginning of the run? [ 6 Answers ]

I want to run 8 new circuits, four 15 amp and four 20amp. Each can be paired with a beginning run of a 14/ 3 or 12/3 wire from the breaker box to a junction box and then can be split off so that a 12/2 or 14/2 wire goes to a recepatcle, or to a device, or to lights. For example one 12/3 wire can...

How to run power from main panel to garage [ 1 Answers ]

I recently build a second separate garage. I have done the interior wiring and was going to upgrade the house service to 400 amps (from 200 amp) and run 200 amps to the garage. The main reason is that the power company did not want to run directly to garage due to 1. having to go around septic...

Does main outlet have to run downhill? [ 1 Answers ]

I just had a new septic tank and leachfield installed. The contractor moved the main outlet (the big pipe that goes through the cellar wall) up. It now exits the cellar 2 feet higher than where it used to exit. 2 days later, I have an odor in the kitchen. I'm worried that, by moving the outlet,...


View more questions Search