    frazwood's Avatar
    frazwood Posts: 129, Reputation: 2
    Junior Member
     
    #1

    May 2, 2010, 04:57 PM
    Connecting to a sewer hub in a basement
    This is somewhat similar to my last question, but it's different enough that I am going to ask about it specifically.

    I am trying to add a second bathroom to a house that was built in 1940. I have most of the waste/vent/drain plumbing figured out, except where I will connect to the sewer hub in the basement floor.

    I have done something like this previously and I purchased a rubber donut that snuggly fit into the sewer hub. This allowed me to connect a 3-inch PVC pipe into the sewer.

    In this case, I bought a 4-inch donut for a 3-inch PVC pipe (i.e. it is a reducing donut hub)... but this is too big for my sewer hub. I then bought a 3-inch donut hub for a 3-inch PVC pipe... and this is too small.

    Are there other sizes available? Where might I find one for purchase? Should I be solving this problem a different way?

    I'll try and post a photo soon.

    Thanks,
    Tim
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    May 3, 2010, 07:42 AM

    Did you lubricate the outside of the 4" donut before inserting it in the hub? The 4: should fit. What's the outside measure of the donut? Let me know, Tom
    frazwood's Avatar
    frazwood Posts: 129, Reputation: 2
    Junior Member
     
    #3

    May 3, 2010, 01:27 PM
    Quote Originally Posted by speedball1 View Post
    Did you lubricate the outside of the 4" donut before inserting it in the hub? The 4: should fit. What's the outside measure of the donut? Let me know, Tom
    My recollection is that the inside diameter of the hub is 4.5 inches. The photograph (which I still need to get off my wife's camera) includes a tape measure... so I can get that.

    What would you use as lubricant? Perhaps that is my problem...

    p.s. This is essentially what I have... although the website claims that there are no standard hub sizes

    Fernco Flexible Donuts, fernco, fernco donut, fernco donuts, Sewer Pipe Compression Joint Donut Seal, Donut Shaped Compression Seal, Sewer Pipe Joint Seal, Pipe Compression Seal, Plumbing Donut Seals | Fernco


    Here is the photograph of the sewer hub.
    Attached Images
     
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    May 4, 2010, 06:13 AM

    What would you use as lubricant? Perhaps that is my problem...
    When we roughed in using dionuts we used Duel-Tite Lubricant , a heavy grease, to make the job easier. Insert the neoprene gasket into the hub. Grease the outside of the gasket before inserting. Now take a file and bevel the sharp edges so the pipe won't hang up on the ridges in the gasket. Next lube the pipe and the inside of the gasket with Dual-Tite Lubricant or a heavy grease. Push the pipe in until it seats on the bottom of the hub. If the pipe's difficult to start it's OK to trim back the first few ridges with a sharp knife. Good luck, Tom
    CHayn's Avatar
    CHayn Posts: 177, Reputation: 10
    Junior Member
     
    #5

    May 5, 2010, 04:20 AM

    Back in the old days they used to install 3.5 inch cleanouts once in a while. I bet Tom remembers those! You may have to lead this one in.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How do I repair a cracked sewer clean out hub? [ 8 Answers ]

I had quite the sewer backup going on last night, had the drain guy out had a great time trying to find the clean out which was under a platform in front of the utility sink in the bathroom. That being said, sewer snaked to 110 feet and toilets flushing and water draining... However, when we looked...

CI pipe no hub joints, is it within code for no hub couplings under ground? [ 4 Answers ]

CI waste lines no hub joints: Is it within the npc to run under ground? Plumbing code no hub coupling joints: Is it within code to use this under ground? I know that in the older days oakum with lead joints were used. Thanks. George

Connecting two computers via ethernet cable ( no hub ) [ 3 Answers ]

I've tried to create a direct computer to computer ( no hub or switch ) ethernet cable network between the main computer which is a Windows XP to a Windows Vista. The connection is never successful. Each time I get " Cable is not connected ( which they are and in good condition )" :confused. Any...

Connecting a PVC to a cast iron hub? [ 1 Answers ]

First of all thanks for the help on my previous question. I found diamond tiped sawsall blade to cut the cracked castiron pipe. But my confidence is still low. I looked at the pipe again to see how far the crack is. The 3" castiron pipe has a vertical crack that goes very close to the castiron hub...

Connecting pvc to pvc with no hub fitting [ 8 Answers ]

My plumber ran into a dilemma when installing rough plumbing for a new basement bathroom. After already laying the pvc piping in place under the broken up concrete floor we found the pvc to cast iron Tee connections leaking. This was discovered after I had filled the opening with a base of gravel...


View more questions Search