New Member
|
|
Apr 25, 2010, 03:21 PM
|
|
Honeywell provision 8000 installation help
I'm trying to install a new VisionPro 8000 but not sure what setting 0701 should be. I have Trane gas furnace and xl13i HP. I have selected 1 heat / 1 cool conventional but it seems there's no delay when swicthing from heat to cool or vise versa making worry it might damage the condenser. I tried to select 2 1 heat/ 1 cool heat pump and seemed both a/c and heat where running at the same time.
Wiring is only 4 wires.
R
Y
W
G
|
|
 |
Uber Member
|
|
Apr 25, 2010, 04:26 PM
|
|
There are lots of Vision Pro models usually beginning with TH8??
What model do you have?
With only 4 wires, it has to be 1 stage heat/cool conventional.
The delay generally only applies to the outdoor unit and not the fan inside. That delay may be settable with another parameter.
|
|
 |
New Member
|
|
Apr 25, 2010, 05:33 PM
|
|
The model number is TH8320U1008
|
|
 |
Ultra Member
|
|
Apr 25, 2010, 05:35 PM
|
|
Did you put it on 1 heat 1 cool conventional?
|
|
 |
New Member
|
|
Apr 25, 2010, 06:02 PM
|
|
That's what it set to now but I have taken it off automatic since there seems to be no delay switching from A/C to heat or vice of versa. Maybe this something I don't need to worry about.
|
|
 |
Ultra Member
|
|
Apr 25, 2010, 06:09 PM
|
|
There should be a separate setting for compressor delay, probably in the 300s of your programing
|
|
 |
New Member
|
|
Apr 25, 2010, 06:23 PM
|
|
Yes, 0580 it's set for 5 minutes. It seems through when I change the thermostate to heat there is no delay for the switch.
|
|
 |
Ultra Member
|
|
Apr 25, 2010, 06:25 PM
|
|
Heat will have no delay as there is nothing on the furnace that requires a delay. The delay is to not short cycle the ac compressor.
|
|
 |
New Member
|
|
Apr 25, 2010, 06:27 PM
|
|
Okay, I'm thinking it must be setup correctly. How would I go about testing the A/C delay time just to make sure?
|
|
 |
Ultra Member
|
|
Apr 25, 2010, 06:34 PM
|
|
When you turn from heat to cool, the stat will either say wait, or the cool on will be flashing instead of staying on solid. This will let you know if you have a delay, also the fan will not start till this delay goes off.
|
|
 |
Uber Member
|
|
Apr 25, 2010, 06:51 PM
|
|
Meaning, only the outside unit will have a delay.
The delay is implemented in the following way.
If power fail, power must be restored for x min before outside unit will turn on.
OUTSIDE unit must be off for x min, before being allowed to turn on which covers the first statement.
Going directly from heat to cool isn't an issue.
|
|
 |
New Member
|
|
Apr 25, 2010, 06:55 PM
|
|
Okay, thanks for the help it does show wait on the display when going from heat to cold.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Honeywell vision pro 8000 installation
[ 1 Answers ]
I have a Trane Model XR 90 High Efficiency, 100,000 BTU’s to heat a two-floor space with about 1900 square feet. When the outside temp. is around 20 degrees F and I set the thermostat to Hold at 63 degrees during the nighttime, when I get up the thermostat is reading 60 degrees. It cannot keep...
Honeywell TH 8000 Day Change
[ 1 Answers ]
How do I change the current day... it shows Tuesday on Monday, etc. How do I change it to Monday?
Wiring a Honeywell ProVision TH8321U1006, upgrade from Weathertron Tstat
[ 0 Answers ]
Saw this link, but didn't fully answer my issue unfortunately: https://www.askmehelpdesk.com/advice/t-323175.html
Wiring question for Honeywell ProVision TH8321U1006, upgrade from Weathertron Tstat
I hope I didn't get in over my head. I'm normally pretty good fixing things around the house...
Trouble with Honeywell VisonPRO 8000
[ 7 Answers ]
Hi, I recently purchased two Honeywell VisonPRO 8000 - TH832U1008 to replace my Honeywell FocusPRO 5000 - TH5220D1003 because I wanted programmable thermostats. After swapping over the connections, the heat function will not work. I can turn on the fan manually, and the cool function works. Outside...
Honeywell VisionPRO 8000 Installation
[ 5 Answers ]
Hi Everyone! We just finished building our new home and didn't think about thermostats along the way. There is a simple digital thermostat installed at this time but we wanted a programmable one. I attempted to install it today but the compressor wouldn't cut on. I've installed thermostats before...
View more questions
Search
|