If the furnace is 80amp how big should the breaker be
It came to our attention about a month ago that we only had 3 of the 4 elements (coils) plugged in properly on our 80 amp furnace. So when the repair man came by to fix our furnace, he mentionned it and reconnected the 4th element but since then every time the furnace starts to heat the house it tripps the breaker in the fuse box. Now when the repair man came back, he said that the breaker in the fuse box was not strong enough to handle the load. So he is basically telling me that I need to get an electrician in here to change both the wireing from the furnace to the fuse box and also the breaker in the fuse box, right now the breaker we have at the moment is a double 70amp breaker. How can I be sure that the breaker is not big enough to handle the load.
|
|
 |
Uber Member
|
|
Apr 20, 2010, 05:18 AM
|
|
An Ampprobe will tell actual Amps.
Wonder if last element was wired correctly?
Does Nameplate give any info?
80 Amps seems large, Is this a Very Large or Very Cold House?
The Breaker should not be Larger than the wire it Protects,
Are they #4's or Larger?
|
|
 |
Uber Member
|
|
Apr 20, 2010, 05:32 AM
|
|
Also, if wires are loose on the Breaker or if the Buss wher the Breaker plugs onto is Burnt or coroded, it can trip at lower amps.
Loose connections generate Heat.
|
|
 |
New Member
|
|
Apr 20, 2010, 05:39 AM
|
|
 Originally Posted by Stratmando
Also, if wires are loose on the Breaker or if the Buss wher the Breaker plugs onto is Burnt or coroded, it can trip at lower amps.
Loose connections generate Heat.
We just had the breaker changed but he replaced the 70 amp breaker with a new 70 amp breaker, then the repair man to us that the breaker was to small to handle the load
|
|
 |
Ultra Member
|
|
Apr 20, 2010, 06:12 AM
|
|
Did the furnace work fine with 3 of the heaters? You may not need to change all the wire inless you was way short on heat.
|
|
 |
New Member
|
|
Apr 20, 2010, 06:20 AM
|
|
 Originally Posted by Joshdta
did the furnace work fine with 3 of the heaters? you may not need to change all the wire inless you was way short on heat.
The house is 5 years old and everything has worked fine until 2 months ago when the furnace caught on fire, that's when the repair man came by and notice that one of the elements was not connected and reconncected it and that's when the situation with the breaker started. The house heats up much faster with all 4 elements. If the wirering was not done properly in the first place I will try to get the electrician that wired the furnace to come basck and do it properly and if he is not around I will get another electrician.
|
|
 |
Ultra Member
|
|
Apr 20, 2010, 06:35 AM
|
|
Did they say what the cause of the fire was? Is your unit capable of have 2 wires? Some units you can run to smaller wires, like 2 40 amp breakers. Some units you can not do it that way.
|
|
 |
New Member
|
|
Apr 20, 2010, 06:44 AM
|
|
 Originally Posted by Joshdta
did they say what the cause of the fire was?? is your unit capable of have 2 wires? some units you can run to smaller wires, like 2 40 amp breakers. some units you can not do it that way.
They did not give a reason they just came and fixed it and that's when they noticed that one of the four elements was not connected.
|
|
 |
Uber Member
|
|
Apr 20, 2010, 06:46 AM
|
|
You may have a short with your Heat strip to Ground if wiring had melted and not corrected. You could look for resistance between the heat strip and ground to determine if you have a short, should be no resistance.
|
|
 |
New Member
|
|
Apr 20, 2010, 07:01 AM
|
|
 Originally Posted by Stratmando
You may have a short with your Heat strip to Ground if wiring had melted and not corrected. You could look for resistance between the the heat strip and ground to determine if you have a short, should be no resistance.
I am not quite sure what that means but the repairman assured me that everything was OK and he is the one that said that my wirering and breaker should be bigger than 70 amp.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
How do you know if your Forced Air Furnace is BIG enough?
[ 4 Answers ]
We purchased a 10 year old home last fall. Since it was build, the lower level was finished off, and two years ago the two-car garage was turned into a mother in law appointment with two rooms, a bathroom, and a kitchen.
It doesn't seem like the existing furnace is forcing enough air out of...
Furnace on a 15amp breaker
[ 7 Answers ]
We purchased a house and have been going through the eletrical and cleaning up some of there "mess" OK lazy ness to make sure evreything is correct. We have the majority of it all cleaned up. However, we came across something that seemed odd. The Furnace (gas) is on a dedicated 15amp breaker. ...
Big bang from furnace on startup
[ 1 Answers ]
Starting this evening my Janitrol furnace is making an exceptionally loud bang. It has repeated the bang every time since at startup. I have disengaged the unit, cleaned the filters and cleaned out the unit, checking the venting for obstructions (haven't seen any). It's late and pretty cold out...
Furnace makes a big boom!
[ 5 Answers ]
Sometimes when my heat kicks on it makes a loud fiery sound like its flame is booming. Hard to explain. Anyone know what I might be referring to?
Must reset furnace breaker to activate
[ 3 Answers ]
I installed a ritetemp digital thermostat and appear to have 2 problems. 1) I’m not getting any ac to the thermostat, so it does not activate the furnace. I know I need to check the 24v transformer and common per the other threads. But, if I go to the circuit breaker panel and reset the furnace (80...
View more questions
Search
|