    How to wire a gfci to a switched half hot/device?
    Say I have a half hot switch and I only want the constant hot side to be protected by the gfci and the other half to be switched, how do I wire this? I have spent hours trying to figure it out already, thanks
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Apr 2, 2010, 04:47 PM

    Several ways, depends if you want the constant load and/or the switched load to be GFI protected.
    No matter what, the loads hot and neutral need to be either on the Line side of the GFI or the Load side. The GFI will trip if the load is not the same on the Hot and the Neutral.
    Not sure what you want protected, but if you wanted the constant hot half unprotected and the switched half protected, you will need to break the neutral tab on the side of the receptacle as well as the tab on the hotside.
    Explain what you want protected, both? We can help.
    teamrandom2222's Avatar
    teamrandom2222 Posts: 4, Reputation: 1
    New Member
     
    #3

    Apr 2, 2010, 04:49 PM

    teamrandom2222's Avatar
    teamrandom2222 Posts: 4, Reputation: 1
    New Member
     
    #4

    Apr 2, 2010, 04:52 PM
    Quote Originally Posted by Stratmando View Post
    Several ways, depends if you want the constant load and/or the switched load to be GFI protected.
    No matter what, the loads hot and neutral need to be either on the Line side of the GFI or the Load side. The GFI will trip if the load is not the same on the Hot and the Neutral.
    Not sure what you want protected, but if you wanted the constant hot half unprotected and the switched half protected, you will need to break the neutral tab on the side of the recepticle as well as the tab on the hotside.
    Explain what you want protected, both? we can help.
    I don't know if the drawing above helps but I want only the constant half to be protected and the switched half to be NOT protected by the GFCI , (PS the above drawing obviously has something wrong to it but its how far I got and what I have now).
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Apr 2, 2010, 04:52 PM

    I don't see the drawing, but you will need 4 conductors from the GFI to the receptacle, The switched half will get its neutral from the Line side of the GFI and the switch will get its hot from the Line side of the GFI, and
    Then you have a hot and neutral from the Load side to the unprotected half.

    If this is romex(12-3), you can'd do it, but with 3 conductors you can protect the constant and switched halfs.
    In that case the neutral tab remains intact, with neutral from load side of GFI to receptacle neutral and the constant hot will be from load side and switch will get power from load side hot as well.
    teamrandom2222's Avatar
    teamrandom2222 Posts: 4, Reputation: 1
    New Member
     
    #6

    Apr 2, 2010, 05:05 PM

    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #7

    Apr 2, 2010, 05:09 PM

    Need to type then click Post quick answer or reply. You'll get it, a little tricky.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #8

    Apr 2, 2010, 05:10 PM

    Granddaughter is going to use computer, will be back later.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #9

    Apr 2, 2010, 07:23 PM

    Here is what I think you said you want to do. Not sure why you would want to do it. I can see splitting the outlet but it should be either GFI protected or it should not. If one half should be GFI protected the other half should be also.
    Attached Images
     

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

220 3 wire to 2 wire device [ 2 Answers ]

The outlet I need to supply has 2 wire plus ground. The feed is 3 wire plus ground. What gets spliced and how?

Adding a GFCI device [ 4 Answers ]

My memory is failing so I'll need to ask for help. I want to ADD a GFCI device into an existing single gang box in the kitchen to provide additional outlets.. Box contains a single pole switch for the overhead light. There are three (3) sets of wires in the box. All three WHITE wires are wire...

GFCI medical device requirements - systems using water [ 3 Answers ]

We are a medical device manufacture, are GFIC receptacles required at a dedicated piece of equipment that is being supply by DI process water and is stationary with cord and plug, need GFIC protection.

Hot/cold Switched, what could be wrong? [ 7 Answers ]

I recently had a bathroom remodel and the plumber may have installed the faucet wrong somehow. The handle is labeled on the right for cold and left for hot. But turning it right results in hot and left, cold. The pipes going into the valve assembly are correct. The plumber insists that the...

Switched outlet is always hot [ 3 Answers ]

I tried to split a switched outlet so the top is always hot and the bottom is controlled by the switch. I snapped the brass connector off and wired the neutral (with black tape) to one of the hot leads with a pigtail. The other neutral went to the silver terminal. Turned the circuit back on and...


View more questions Search