        Breaker question
       
                  
        I have a sub panel (125 Amp Main Lug Load Center) with this Siemens Q21525CT breaker (15/25/25/15 Amp). It's a quad/tandem breaker with two 25Amp breakers common trip. This 25amp common trip is for 2 duplex 220v receptacles (4 outlets) for 4 - 600 watts HID lights which equals 11 amp @ 220v and 2 duplex 5-15 (each one on a 15amp breaker) for 110v (1,000 watts or less for miscellaneous in one 15amp and 800 watts 5000 BTU A/C at the other one). I plan to feed this sub panel with a 30amps double pole breaker. My question is… if I’m only using 11 amps @ 220v that means I have 49 amps for use @ 110v or 19amps only?:confused:
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Uber Member |  | 
 
                  
                      Mar 31, 2010, 02:39 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Your post is confusing, so I'll try to explain it this way:
 
 Suppose you have a 30A 240 Breaker
 Power is constant, so you have available 30*240 Watts or
 120*30A + 120 *30A which is 30A per 120 V leg.
 
 When you have only a 240 V load connected, there is no neutral current.
 
 If you have a 20A on one 120 V leg and 10 amp on the other 120 V leg and a 5 A 240 V load connected to this breaker you have:
 
 20+5 on one 120 V leg
 10A + 5 on the other 120 V leg
 
 And (25-15) or 10A flowing in the neutral.
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Mar 31, 2010, 04:21 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        
	
		
			
			
				
					  Originally Posted by KeepItSimpleStupid   Your post is confusing, so I'll try to explain it this way:
 Suppose you have a 30A 240 Breaker
 Power is constant, so you have available 30*240 Watts or
 120*30A + 120 *30A which is 30A per 120 V leg.
 
 When you have only a 240 V load connected, there is no neutral current.
 
 If you have a 20A on one 120 V leg and 10 amp on the other 120 V leg and a 5 A 240 V load connected to this breaker you have:
 
 20+5 on one 120 V leg
 10A + 5 on the other 120 V leg
 
 and (25-15) or 10A flowing in the neutral.
 I'm using 10/3 to feed this sub panel. Sorry for the confusion Sir. I read at the internet 30amp @ 220v = 60amp @ 110v. My question is if I'm using only 12 amp @ 220v for my lights it that’s means I can use 36 amp (18 x 2) because it’s for 110v or its only 18 amp left for 110v receptacles? Sorry Sir if this doesn't make sense at all
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Uber Member |  | 
 
                  
                      Mar 31, 2010, 05:30 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        OK, I think I get it.
 
 Fed from a 25 A breaker at 240 V
 
 12 A  at 240 V for HID lighting.
 
 So you have 25-12 or 13 Amps available at 120 from both poles.
 
 Thus you have potentially two circuits with 13 A available at 120 V.
 
 Are we on the same page?
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Apr 1, 2010, 04:47 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        
	
		
			
			
				
					  Originally Posted by KeepItSimpleStupid   OK, I think I get it.
 Fed from a 25 A breaker at 240 V
 
 12 A  at 240 V for HID lighting.
 
 So you have 25-12 or 13 Amps available at 120 from both poles.
 
 Thus you have potentially two circuits with 13 A available at 120 V.
 
 Are we on the same page?
 
I want to feed my sub panel with a 30 amps double pole circuit with 10/3 from my main panel.  My sub panel has a quad/tandem breaker with two 25Amp breakers common trip for 220v and two 15Amp for 110v. Here is the sequence 15/25/25/15. My lights they are going to use 12 amps from this 30a circuit. That means I can use 18 amps for 110v? Or 36amp because they are only using only 110v? I read at the diy forums that 30amp at 220v = 60amp at 110v
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Apr 2, 2010, 07:10 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        
	
		
			
			
				
					  Originally Posted by editon69   I want to feed my sub panel with a 30 amps double pole circuit with 10/3 from my main panel.  My sub panel has a quad/tandem breaker with two 25Amp breakers common trip for 220v and two 15Amp for 110v. Here is the sequence 15/25/25/15. My lights they are going to use 12 amps from this 30a circuit. That means I can use 18 amps for 110v? or 36amp because they are only using only 110v?. I read at the diy forums that 30amp at 220v = 60amp at 110v I found the answer: I have 5760 watts total, to play with safely, regardless of what voltage. 30a*0.8 = 24a*240 = 5760 watts for constant use
     |  
    |  |  
 
 
 
  
    | Question Tools | Search this Question |  
    |  |  |  
 Add your answer here.
 
Check out some similar questions!
Question on proper use of GFIC breaker
 [ 1 Answers ]
I had some outdoor receptacles recently installed and would like to know if it is proper to put a GFIC breaker in the panel for this circuit and will it protect the receptacles from shorting instead of putting a GFIC receptacle in the circuit?
 
Breaker question?
 [ 6 Answers ]
How is everyone one doing? I am new to this site seems like there a lot of good information on hear.  So I own my home.  I was just curious is per say I have three 15amp breakers, Can I just swap those 15amp breakers with 20 amp breakers or do I have do do some wiring.  Hence need an electrician? ...
 
Breaker Box Question
 [ 5 Answers ]
I guess it would be better to call it a fuse box... not breaker. 
 