Breaker question
I have a sub panel (125 Amp Main Lug Load Center) with this Siemens Q21525CT breaker (15/25/25/15 Amp). It's a quad/tandem breaker with two 25Amp breakers common trip. This 25amp common trip is for 2 duplex 220v receptacles (4 outlets) for 4 - 600 watts HID lights which equals 11 amp @ 220v and 2 duplex 5-15 (each one on a 15amp breaker) for 110v (1,000 watts or less for miscellaneous in one 15amp and 800 watts 5000 BTU A/C at the other one). I plan to feed this sub panel with a 30amps double pole breaker. My question is… if I’m only using 11 amps @ 220v that means I have 49 amps for use @ 110v or 19amps only?:confused:
|
|
 |
Uber Member
|
|
Mar 31, 2010, 02:39 PM
|
|
Your post is confusing, so I'll try to explain it this way:
Suppose you have a 30A 240 Breaker
Power is constant, so you have available 30*240 Watts or
120*30A + 120 *30A which is 30A per 120 V leg.
When you have only a 240 V load connected, there is no neutral current.
If you have a 20A on one 120 V leg and 10 amp on the other 120 V leg and a 5 A 240 V load connected to this breaker you have:
20+5 on one 120 V leg
10A + 5 on the other 120 V leg
And (25-15) or 10A flowing in the neutral.
|
|
 |
New Member
|
|
Mar 31, 2010, 04:21 PM
|
|
 Originally Posted by KeepItSimpleStupid
Your post is confusing, so I'll try to explain it this way:
Suppose you have a 30A 240 Breaker
Power is constant, so you have available 30*240 Watts or
120*30A + 120 *30A which is 30A per 120 V leg.
When you have only a 240 V load connected, there is no neutral current.
If you have a 20A on one 120 V leg and 10 amp on the other 120 V leg and a 5 A 240 V load connected to this breaker you have:
20+5 on one 120 V leg
10A + 5 on the other 120 V leg
and (25-15) or 10A flowing in the neutral.
I'm using 10/3 to feed this sub panel. Sorry for the confusion Sir. I read at the internet 30amp @ 220v = 60amp @ 110v. My question is if I'm using only 12 amp @ 220v for my lights it that’s means I can use 36 amp (18 x 2) because it’s for 110v or its only 18 amp left for 110v receptacles? Sorry Sir if this doesn't make sense at all
|
|
 |
Uber Member
|
|
Mar 31, 2010, 05:30 PM
|
|
OK, I think I get it.
Fed from a 25 A breaker at 240 V
12 A at 240 V for HID lighting.
So you have 25-12 or 13 Amps available at 120 from both poles.
Thus you have potentially two circuits with 13 A available at 120 V.
Are we on the same page?
|
|
 |
New Member
|
|
Apr 1, 2010, 04:47 PM
|
|
 Originally Posted by KeepItSimpleStupid
OK, I think I get it.
Fed from a 25 A breaker at 240 V
12 A at 240 V for HID lighting.
So you have 25-12 or 13 Amps available at 120 from both poles.
Thus you have potentially two circuits with 13 A available at 120 V.
Are we on the same page?
I want to feed my sub panel with a 30 amps double pole circuit with 10/3 from my main panel. My sub panel has a quad/tandem breaker with two 25Amp breakers common trip for 220v and two 15Amp for 110v. Here is the sequence 15/25/25/15. My lights they are going to use 12 amps from this 30a circuit. That means I can use 18 amps for 110v? Or 36amp because they are only using only 110v? I read at the diy forums that 30amp at 220v = 60amp at 110v
|
|
 |
New Member
|
|
Apr 2, 2010, 07:10 AM
|
|
 Originally Posted by editon69
I want to feed my sub panel with a 30 amps double pole circuit with 10/3 from my main panel. My sub panel has a quad/tandem breaker with two 25Amp breakers common trip for 220v and two 15Amp for 110v. Here is the sequence 15/25/25/15. My lights they are going to use 12 amps from this 30a circuit. That means I can use 18 amps for 110v? or 36amp because they are only using only 110v?. I read at the diy forums that 30amp at 220v = 60amp at 110v
I found the answer: I have 5760 watts total, to play with safely, regardless of what voltage. 30a*0.8 = 24a*240 = 5760 watts for constant use
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Question on proper use of GFIC breaker
[ 1 Answers ]
I had some outdoor receptacles recently installed and would like to know if it is proper to put a GFIC breaker in the panel for this circuit and will it protect the receptacles from shorting instead of putting a GFIC receptacle in the circuit?
Breaker question?
[ 6 Answers ]
How is everyone one doing? I am new to this site seems like there a lot of good information on hear. So I own my home. I was just curious is per say I have three 15amp breakers, Can I just swap those 15amp breakers with 20 amp breakers or do I have do do some wiring. Hence need an electrician? ...
Breaker Box Question
[ 5 Answers ]
I guess it would be better to call it a fuse box... not breaker.
I live in a rather old house with k&t wiring. Our box, located in the basement, has all the wiring come in from the top. At the top of the front panel there are two black pull-out things that have markings saying main and off. They...
Question on 12 gauge w/ 15 amp breaker
[ 2 Answers ]
Hello,
Glad to have found this place.
Just had a question regarding 12 gauge wiring. While I know it is unsafe to use 15 gauge for a 20 amp breaker, are there any safety concerns using 12 gauge wire on a 15 amp circuit breaker? Reason I ask is I had recessed lights put in my basement and had...