    Can you splice into an existing ground wire to add a receptacle?
    Adding a receptacle with two wire system, can I splice into an existing ground wire to ground my neew receptacle?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    Mar 8, 2010, 05:22 PM
    Quote Originally Posted by chazz79 View Post
    can I splice into an existing ground wire to ground my neew receptacle?
    What does that mean? If you have a 2-wire system, meaning your cable is 2-wire without a ground, you do not have a ground wire to splice into.

    If you question is "How do I replace a ungrounded receptaclel (two holes) with a grounded receptacle (three holes)". The answer is you replace it with a GFI receptacle. The GFI is not grounded and you mark it "Ungrounded".
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Mar 9, 2010, 06:44 AM
    This can be confusing, so I often don't mention this,

    You can extend a 2 wire cable to a new receptacle, and then ground the new receptacle to the grounding electrode system, which means you run a green wire from the new outlet to either the ground rod, or the incoming water line, no farther thant five feet from point of entry into the building, or a few other locations, but not connect to any grounding conductor.

    My stance is, if you can run a ground wire from a n ew receptacle, you can run a new feeder to the panel, and have the new outlet grounded properly with a new 3 wire cable.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I butt splice a main breaker ground wire to make it longer [ 9 Answers ]

The ground wire that comes from the meter to the main breaker is too short for the new box I want to install. Can I butt splice the ground to make it longer. This is the 4.0 ground and is about 18" short

Changing old receptacle, no ground wire, wires doubled up [ 1 Answers ]

I am changing a 120v receptacle in an old house, have found that there is no ground wire. The receptacle has two black and two white wires, each of which is on the same screw of the old receptacle, though the book I'm using seems to say they should be on different screws. Can I safely instal a new,...

Can I splice off 1 wire to create 2 separate wire connections for 2 ceiling fans [ 10 Answers ]

I'm planning on installing 2 ceiling fan, 1 in each of 2 bedrooms. There's no electrical on the ceilings and need to come down from the attic. The attic has several different white plastic contained wires running throughout the attic. I'm wondering if I should splice from 2 separate sources, or...

Replacing 2-prong receptacle with 3-Prong -NO GROUND WIRE [ 6 Answers ]

Hi there! I was wondering if someone can tell me how exactly I go about doing this safely. I have an existing 2 prong ungrounded plug... theres no ground to this receptacle... old metal box does not seem to be grounded either. I would like to replace this receptacle with a 3 prong GFCI...


View more questions Search