    Symptoms of a 200amp main zinco service breaker going bad
    What are the symptoms of a 200 amp zinco service breaker going bad? Our lights are surging when major appliances run. PG&E (power company) came out and checked and there was not a bad neutral and connections are good. Thanks for any advice.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 6, 2010, 05:09 AM
    OK need to go over the word surge, and the symptoms. Surge would mean voltage swell, or increase in voltage, and the lights would get brighter. This can be caused by a broken neutral in a 3 wire feeder, just like the feed from the utility.

    If the lights are dimming when the appliance starts, that is a voltage sag, or a decrease in voltage. This can be due to voltage drop caused by a loose or corroded connection, or contact points in a circuit breaker.

    Zinsco breakers are not too popular on the east coast, at least what I have seen.

    I do recall an issue with Zinsco:

    Zinsco Sylvania Kearney Electrical Panel and Circuit Breaker Hazards, Failures, Inspection, Detection, Repair, Replacement - Sylvania Zinsco circuit breakers and panel hazards

    There are ways of confirming bad contacts in a circuit breaker, but a service electrician that has special equipment, such as a DLRO, Digital Low Resistance Ohm-Meter, or a Milli-volt-Meter, needs to test the unit.

    Would be a waste of money testing a unit that already has a known problem. Money better spent on replacing the panelboard.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can you have a higher main breaker then what your service is [ 1 Answers ]

I currently have a 200 amp service. I ordered a panel which I thought was a QO140M200 and instead received a QO140M225. Will this still work for a 200 amp service? The only reason I'm having the panel changed is because (1) it's a rats nest inside and (2) it's full considering it's only 30 space.....

Can I tapinto the line side of a100 amp main breaker to feed a 60 amp breaker service [ 1 Answers ]

Can I tap into the line side of a 100 amp main breaker to feed a 60 amp breaker for a electric stove

Got a 200amp service can I run another two 50amp breaker in the 200amp service [ 0 Answers ]

I got a 200amp service put in and I'm trying to get a electric stove in the basement will that 200amp service be enough power for two stove or will I have to run a sub-panel

Size of main breaker and service entrance cable [ 1 Answers ]

Hi, I am new on this site. I just want to know what is the minimum size of service entrance conductor and main breaker for 17 lighting outlets and 15 conveniece outlets plus one 1.5Hp aircon and 2000 heater. Your reply would be highly appreciated. Thank you.


View more questions Search