    White-Rodgers 1F80-51 wiring
    I have a Rheem heat pump unit. A White-Rodgers 1F80-51 thermostat was connected up with the A/C cooling cycle working, but for heat, only the strip elements in the air handler come on. The thermostat is wired; white to W, red to RH w/jumper to RC, blue to B, nothing to O, yellow to Y, green to G, and a brown wire to Nothing.

    I have two experts saying the following; the thermostat is just wired wrong, while another is stating the thermostat is just incompatible with the Rheem and must be changed out.

    Suggestions/help please,

    Michael
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 17, 2010, 09:20 AM
    Quote Originally Posted by FL09MRM View Post
    I have a Rheem heat pump unit. A White-Rodgers 1F80-51 thermostat was connected up with the A/C cooling cycle working, but for heat, only the strip elements in the air handler come on. The thermostat is wired; white to W, red to RH w/jumper to RC, blue to B, nothing to O, yellow to Y, green to G, and a brown wire to Nothing.

    I have two experts saying the following; the thermostat is just wired wrong, while another is stating the thermostat is just incompatible with the Rheem and must be changed out.

    Suggestions/help please,

    Michael

    The stat is only for one stage heat and I believe you need 2 stage since the outside HP needs one and the electric strip elements need another.
    Read for yourself

    http://www.white-rodgers.com/wrdhom/.../0037-5285.pdf
    tlcarrig's Avatar
    tlcarrig Posts: 2, Reputation: 1
    New Member
     
    #3

    May 7, 2010, 07:42 PM

    hvac1000, you might have an interesting read there but I'm getting a "page cannot be found" error. How about checking on this.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    May 8, 2010, 03:56 AM
    Emerson has taken over the White Rodgers info area so the link has changed. Try this.

    http://www.emersonclimate.com/Docume.../0037-5285.pdf

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hook Up of White Rodgers 1F80-261 Thermostat [ 3 Answers ]

I have a gas furnace with only 2 wires running to a mechanical thermostat. When heat is off, Voltage is about 25 volts AC mesured at thermostat. When heat is on, voltage measured at thermostat is 0 volts AC. Need to know if I can replace old mechanical thermostat with White Rodgers 1F80-261...

White-Rodgers 1F80-54 manual [ 2 Answers ]

How do I get a manual for the White-Rodgers 1F80-54 manual?


View more questions Search