    Can you install more than one 240 volt heaters on a breaker
    We are trying to update the heaters in our house and currently have baseboard heat and were going to use the Cadet wall heaters. Currently all the heaters in the house are on 1 breaker (10 baseboard) is that safe should we split them up as we update?
    tk03's Avatar
    tk03 Posts: 33, Reputation: 2
    Junior Member
     
    #2

    Feb 16, 2010, 05:54 PM

    Yes, depending on the size of the breaker. 10 may be overdoing it.
    Add up all the watts and divide by voltage. Usually 240v. You must be at least I believe it is 10% under that rating.
    If you have 10000 watts adding all the heaters together and the voltage is 240v (measure to be sure).
    10,000/240 = 41.6 amps. Must use a 50 amp breaker. The second problem is wire size. A 10 ga. Wire will only do 30 amps, 12 ga will do 20 amps.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Required circuit breaker size for 240 volt dayton 3UG73 electric heaters [ 11 Answers ]

What size breaker should be used for a dayton 3UG73 electric heater , wired for 240 volts

Connecting 120/240 volt line to light, gfci and pool pump breaker [ 15 Answers ]

I have recently demolished my shed and long with it the electrical connections which powered my light switch, gfci receptical and pool pump. I thought I had the electrical connections correct but the breaker is tripping when I attempted to turn it back on. Breaker is 15 Amp The line coming...

240 volt breaker not working [ 2 Answers ]

Hi guy, I got a ballast that work on 120volt and 240 volt, I use NC230 from stab-lok on my stab-lok panel When I plug the ballast on 120v black wire on breaker , white on neutral bar and ground... on ground bar.. the ballast works perfectly... When I set the ballast to 240V ( its just a...

Electric 240 Volt Wall Heaters [ 1 Answers ]

On on 30-amp 240V circuit I have (2000w, 1500, 1500, and 500w wall heaters) which adds up to 5500 walts. Two wire are going to the breaker Black, Red, and then the ground. If both the red and black are hot shouldn't there be a white for the return or to complete the circuit.

Can I connect a 240 volt electric range to a 30 amp breaker [ 1 Answers ]

I'm renovating a rental unit and removed a 3 in one appliance (bar fridge/2 stove elements/sink). It was hooked up to 10/3 copper wire on a 30 amp breaker. I want to install a 24 inch electric stove/oven in it's place. I want to hook up a 24 inch electric stove/range to 10 gauge 3 copper wire...


View more questions Search