    What wattage is needed for a 230 volt 3\4 horsepower submersible well pump
    What size generator would be needed to run a 1 hp submersible well pump ?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 10, 2010, 11:36 AM
    You mention 3/4 HP in the title, and 1 HP in the post.


    Motors pose an issue, that they draw much more to start. Called Locked Rotor Amperage (LRA), than once running, call Running Load Amperage (RLA)

    According to NEC, a 1 HP 230 Volt motor has an RLA of 8 amps and a LRA of 48 Amps.

    Any genset needs to be able to provide the peak power to start a motor.

    So, using P=EI, 230 V x 8= 1840 watts, and 230 x 48 = 11,040 watts.

    But, wait, these are not proper calculations for motor watts.


    Missing a Code letter that should be on the pump nameplate or datasheet.

    See attached chart, you will notice Code Letters for certain motors.

    The Code Letter will relate to Table 430.7(B) in the National Electric Code.

    SIZING A GENERATOR FOR HOME USE

    Any genset will need to be overcome the LRA of a motor.

    Hope this helps, as I realize this is as clear as mud.

    Get back with the Code Letter and we should be able to get you a size.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I operate 230 volt machinery with 480/277 volt [ 7 Answers ]

480/277 volt 3 phase power is the proposed electrical service for a for a new building. Will I be able to power machinery that requires 230 volt 3 phase?

115/230 volt wiring [ 11 Answers ]

I bought a beautiful chandelier at a garage sale at a great price. Can the chandelier be wired for 230 volts for use in the Philippines as long as 230 volt bubs are used?

230 volt DC lathe motor [ 16 Answers ]

I recently purchased a new german made lathe with a 1 and 1/2 h.p. single phase DC motor rated at 1400 watts at 2800 rpm, the plate on the motor says 60 hertz. 6 amp nominal consumption 230 volts. I also purchased a 110volt to 220 volt step-up transformer rated at 2300 watts. The lathe has a...

230 volt Motor wiring [ 11 Answers ]

I have a 6 hp 230 volt air compressor motor that I have wired on a twin 20 amp breaker with a 10/2 wire. I cannot get the motor to start, I have took it off and had it checked and it works fine, just not when I wire it up in my garage. I do have power at my 10/2 wire, and cannot understand why it...

3 phase 230 volt panel [ 4 Answers ]

I have a 3 phase 230 volt 3 wire panel that has a 120, 120 & 208 volts phase to ground and 230, 230, & 230 phase to phase.The AC guy came and installed a new 208/230 volt 3 phase unit. He measured above voltages and told me since one of the voltages is 208 we have to fix that problem first. Do you...