    Basement Circuit Plan
    Hello,

    What a great forum! I have a circuit plan for my basement, and I want to get some input from professionals. I do plan to hire a contractor, but want to make sure my plan is sound.

    Floor Plan



    Circuit Plan

    Bathroom/Kitchenette
    - 1 15 amp dedicated for vanity light/overhead light/closet light, 3 sconces in rec room, under cabinet lighting in kitchenette - max 1000W
    - 1 20 amp dedicated for 5 outlets in kitchenette/bathroom area
    Lobby - GFI circuit breaker
    - existing circuit, tie basement light into 1 sconce, add 5 outlets
    Main room/bedroom/closet - max 500W
    - 1 20 amp dedicated for 14 bedroom & rec room outlets -
    - 1 15 amp dedicated for 14 can lights - max 1200W
    Main HT
    - 1 20 amp for 6 zones of lighting wired to Grafik Eye (7 soffit cans, 6 sconces, rope, riser, 3 stage front, 3 stage rear) - max 1800W
    - 1 20 amp for outlets (riser 2, columns 6, stage 1, projector box fan 1)
    Equipment Room
    - 1 20 amp for 2 outlets - 1 powerbridged switched outlet for projector & 2 powerbridged switched outlets on stage for subs - max 1200W
    - 1 20 amp for 3 outlets - max 1500W
    Storage room east
    - 1 20 amp for storage room work bench area - 4 outlets, shop light, Equip room light - max 1500W

    Any comments, questions or criticism is welcome!

    Thanks,
    Bill
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 2, 2010, 06:43 AM
    My commnets follow each statement in red:

    Circuit Plan

    Bathroom/Kitchenette
    - 1 15 amp dedicated for vanity light/overhead light/closet light, 3 sconces in rec room, under cabinet lighting in kitchenette - max 1000W

    Circuit is fine, Need AFCI circuit breaker for this.

    - 1 20 amp dedicated for 5 outlets in kitchenette/bathroom area
    Lobby - GFI circuit breaker

    Kitchen circuits/outlets must be dedicated for kitchen.
    bathrrom circuit must be dedicated for bathroom(s) only.

    - existing circuit, tie basement light into 1 sconce, add 5 outlets

    OK, just be sure existing circuit can handle added load.


    Main room/bedroom/closet - max 500W
    - 1 20 amp dedicated for 14 bedroom & rec room outlets -
    Perhaps a separate circuit for each room. Need AFCI
    - 1 15 amp dedicated for 14 can lights - max 1200W

    OK need AFCI

    Main HT
    - 1 20 amp for 6 zones of lighting wired to Grafik Eye (7 soffit cans, 6 sconces, rope, riser, 3 stage front, 3 stage rear) - max 1800W
    OK need AFCI

    - 1 20 amp for outlets (riser 2, columns 6, stage 1, projector box fan 1)
    OK need AFCI

    Equipment Room
    - 1 20 amp for 2 outlets - 1 powerbridged switched outlet for projector & 2 powerbridged switched outlets on stage for subs - max 1200W
    - 1 20 amp for 3 outlets - max 1500W
    OK need AFCI

    Storage room east
    - 1 20 amp for storage room work bench area - 4 outlets, shop light, Equip room light - max 1500W
    OK need GFI for all receptacles.

    Me personally would be using all #12 wire and 20 amp circuits for the entire project as minimum.

    Dont forget smoke detectors, one in the bedroom, and at least one in the common area outside bedrooms, interconnect with others in the home.

    Thas all I see at the moment.
    schmidtwi's Avatar
    schmidtwi Posts: 3, Reputation: 1
    New Member
     
    #3

    Feb 2, 2010, 07:02 AM
    Thank you sir! I will isolate the kitchen and bathroom area. Can I combine lighting & circuits on the same circuit for each room with GFI breaker? (1 circuit each?)

    I plan to use AFCI for all non GFI breakers. Will also GFI for the work bench area.

    May just up everything to 20 amp also. Appreciate your help!
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Feb 2, 2010, 10:42 AM

    A couple of things:

    Rethink shop lighting. It's not a good idea to have the whole room go dark when using a power tool. Lighting not combined with outlets makes sense in some cases.

    I will also suggest wiring the switches with ?/3 view to allow the use of automation devices that may require a neutral.
    schmidtwi's Avatar
    schmidtwi Posts: 3, Reputation: 1
    New Member
     
    #5

    Feb 2, 2010, 12:13 PM
    Thanks for the input, KISS. The shop lights I have come with a standard 3 prong plug, so I plan to use one of the 20 amp outlets for that anyway. The shop is also a storage room, with other lights attached to another circuit. I may use this circuit for a light right over the shop section.

    I do plan to use 12/3 or 14/3 for most switches.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Basement bathroom plumbing plan [ 4 Answers ]

Hi everyone, happy new year. I am planning on adding a small, full bathroom in the corner of the basement. There is an existing sewage ejection pit for the floor drain and I plan on breaking out concrete and tying into it with a 3" PVC waste line. I want to be sure the plumbing is vented...

Circuit planning for basement. [ 4 Answers ]

So, I've been finishing my basement, and need to make some final decisions on the electric stuff. I've tossed around a few different ideas for the circuits, but can't decide. When my home was built the outlets and lights in rooms were all put on the same circuit. For example, bed 2&3 are on 1-15A...

Basement Bathroom Plan.Will it work? [ 4 Answers ]

I am adding a bathroom in my basement. I have searched and read quite a bit of postings in the plumbing section of this website and came up with a plan on how to proceed. I have a few questions and also would like to present my ideas I came up with after reading old postings and have someone tell...

Retail Store Basement Electrical Plan [ 5 Answers ]

I have a couple questions regarding an electrical plan for the basement below a retail store for it to meet NEC 2005. The 2 stairways are over 6 steps each and go upstairs to the retail space, not to the exterior of the building. 1. Are there any rules pertaining to location of recepatcles for...

Basement Circuit Layout [ 9 Answers ]

I'd like to run my circuit layout by everyone for feedback. I am finishing my basement, including a bedroom, bathroom, and a large open room which includes a wetbar, home theater, and kids/craft area. The total finished area is about 775 sq. ft. We have 200 amp service and 3 open breaker slots,...


View more questions Search