    Rough in a downstairs half-bath
    Getting ready to try to install a half bathroom in basement, seems the builder anticipated this when building, problem is this, the stack runs pretty close to where I want to install toilet, (within 3 ft), they also included another drain with a cap on it about a foot from where toilet will be(to close to wall to use as toilet drain), I am confident enough to tap into it but lost on venting procedures and which one to tap into. the drain for sink is in place and capped off so that shouldn't be a problem.Thanks
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Feb 1, 2010, 09:23 PM

    It is very likely already vented. Can you post a picture of what you have?
    vaccarodm's Avatar
    vaccarodm Posts: 11, Reputation: 2
    New Member
     
    #3

    Feb 1, 2010, 11:30 PM
    Hope this helps, I will try to explain what all it is, the stub out is what I am wanting to tap into (easy to get to).. the others are what it all looks like up top, another thing that may also be relevant is this is considered a basement, however, it is a tri-level house and there is a basement lower than this one (all be it on the other side of house) that has the washer/dryer/ floordrain and multiple stub outs in place, my biggest fear is putting this in and it not draining to properly. Thanks, and I included one of where I plan to put sink
    Attached Images
         
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #4

    Feb 2, 2010, 06:01 AM
    Vaccarodm:

    I'm pretty sure that the capped pipe is for the toilet and the pipe over by the sink is the toilet vent. The sink vent and the toilet vent connect together in the pic. And go upward.

    It all looks to be done for you..?

    How far is the pipe with the cap off the wall to the center of the pipe? Let us know...

    MARK
    vaccarodm's Avatar
    vaccarodm Posts: 11, Reputation: 2
    New Member
     
    #5

    Feb 2, 2010, 08:05 AM
    The capped pipe is actually built int wall almost, hopefully pic attaches
    Attached Images
     
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #6

    Feb 2, 2010, 08:24 AM
    The capped pipe is the toilet drain. The wall got built around it... ;)

    Here, I would recommend that you chip up the concrete and expose the piping back to where you want to install the toilet. If you are lucky, you can simply cut the pipe underground and install an elbow fitting... stub pipe up "dry fit" (don't cement/glue the stub up pipe)... install some cardboard around the pipe (so equals 1" thick) and then recement the floor. Later, when the floor is finished, you will remove the cardboard and the dry fit pipe and then measure pipe needed and install a new closet flange.

    The venting should be all set underground unless the fitting is where you want the toilet to go and then the vent fitting will need to be moved further back and connected back onto the vent line underground.

    No vent work needed above the floor.

    MARK
    vaccarodm's Avatar
    vaccarodm Posts: 11, Reputation: 2
    New Member
     
    #7

    Feb 2, 2010, 08:48 AM

    The center of closet flange will be approx 15 inches from wall (will get toilet and "dry set" to make sure that's where I want it first), I will chip up floor to existing stub, glue in elbow, glue in horrizontal pipe, dry fit stub leading down to horizontal (so I know what length is needed after floor is re-poured) wrap with the cardboard so I don't concrete the "dry" pipe in so I can pull it back out, pour floor, measure and be in business?
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #8

    Feb 2, 2010, 09:20 AM
    The center of the closet flange wants to be exactly 12" from the rough stud wall....will leave you with 11.5" from the sheetrock at finish. This measure works best for 99% of all standard 12" rough in toilets. Otherwise, you understood perfectly!

    MARK
    vaccarodm's Avatar
    vaccarodm Posts: 11, Reputation: 2
    New Member
     
    #9

    Feb 2, 2010, 09:38 AM

    Thank you SO much!
    pattyg2's Avatar
    pattyg2 Posts: 480, Reputation: 27
    Full Member
     
    #10

    Feb 2, 2010, 12:15 PM
    Thanks for helping this guy out Mark! I recommended askmehelpdesk to him from Yahoo Asks. He got a much better answer here!
    Patty
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #11

    Feb 2, 2010, 05:48 PM
    Thank you Patty... always a pleasure running into you... :) It's nice that you took the time to help, too!

    Vaccarodm... if you are around let me know I want to draw up what I think you'll find underground... let me know when you pop back in by posting here. Thanks...

    Mark
    pattyg2's Avatar
    pattyg2 Posts: 480, Reputation: 27
    Full Member
     
    #12

    Feb 2, 2010, 06:21 PM
    Name:  DSC04270.jpg
Views: 881
Size:  67.2 KB

    Name:  DSC04269.jpg
Views: 875
Size:  58.8 KB
    Quote Originally Posted by massplumber2008 View Post
    Thank you Patty....always a pleasure running into you...:) It's nice that you took the time to help, too!

    Vaccarodm...if you are around let me know I want to draw up what I think you'll find underground....let me know when you pop back in by posting here. Thanks...

    Mark
    I will always remember the help you gave me to do my bathroom annd my son's now. It's coming along OK and I even made them make the tile guy give them a niche which he didn't want to do!
    vaccarodm's Avatar
    vaccarodm Posts: 11, Reputation: 2
    New Member
     
    #13

    Feb 3, 2010, 06:16 PM

    Thank you Patty and Mark!. you guys helped out more than you will ever know! Finished wiring today and will tear into plumbing this weekend!
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #14

    Feb 3, 2010, 06:27 PM
    Glad to help! Patty's really something... huh? Check out her previous projects by clicking on her name... see options.

    Otherwise, check back tomorrow and I'll draw up what I expect you to find underground.

    Just post an OK so it'll show up to remind me in the AM?

    Thanks...
    vaccarodm's Avatar
    vaccarodm Posts: 11, Reputation: 2
    New Member
     
    #15

    Feb 3, 2010, 07:14 PM

    O.K thanks again
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #16

    Feb 4, 2010, 06:46 AM
    Hi... just wanted to present what I think is under that floor.

    Open the hole up pretty big as indicated in the drawing... it will save time in the long run. Cut out the necessary pipes and install a new 3" coupling onto the old pipe. Next, you'll install a 3"x2" wye fitting and a street 45 to pick up the two inch vent with a new 2" elbow and 2" coupling. Use a 3" elbow to stub up the dry fit pipe... cardboard around and then you can run a hose down the toilet elbow to check for leaks.

    Backfill the trench and reconcrete the floor.

    Let us know how you make out...

    MARK
    Attached Images
     
    vaccarodm's Avatar
    vaccarodm Posts: 11, Reputation: 2
    New Member
     
    #17

    Feb 12, 2010, 01:56 PM

    Started breaking concrete, got a little nervous of hitting pipes underneath, pulled cap off stub out and it goes down about a foot and elbows AWAY from the stack! Thinking it may be time to call in a pro?
    Attached Images
     
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #18

    Feb 13, 2010, 09:43 AM
    I don't know...

    I'm thinkin' even if the pipe goes that way it shouldn't make a difference in doin' this yourself...

    Here, you start chipping into the concrete about 1 foot away from where you think the pipe is... chip away at the concrete only... don't let the jackhammer punch deep through so it can break the pipe. Take your time, create a hole and then UNDERMINE the concrete by pulling dirt and rocks out. As you undermine the concrete you can feel for the pipe before chipping out the next section of concrete...

    In this manner, you work toward the pipe until it is located and then just work forward from there.

    Hope that made sense... hope it helped!

    MARK
    vaccarodm's Avatar
    vaccarodm Posts: 11, Reputation: 2
    New Member
     
    #19

    Feb 13, 2010, 10:00 AM

    It does make sense, my fear is where is this pipe running to, I know it eventually has to go in to the main stack somewhere, but on this floor there is a few ground drains with grates on them (in garage,and by water heater) my fear is that "waste" will be going through these lines and have a smell coming up through them, sounds crazy I know, my wife says I am thinking too much and in her opinion, making it harder than it needs to be.lol
    massplumber2008's Avatar
    massplumber2008 Posts: 12,832, Reputation: 1212
    Senior Plumbing Expert
     
    #20

    Feb 13, 2010, 11:48 AM
    Mmmm... possible I suppose, but unlikely that sewer would be too much of an issue even if you did run into trouble... just stop using the drain pipes and no more sewer issues...

    Most likely you'll find the pipes and then repipe them as needed. The extra nice thing here is that they are plastic pipes... much easier than the old cast iron piping would have been... ;)

    I'd give it a shot and if you get into anything questionable you know you can pop back here and work through it!

    Keep us posted.

    MARK

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

My downstairs half bath light was flickering and now it will not turn on at all. [ 4 Answers ]

The light was flickering and it went out so I thought it was the bulb and changed it. The new bulb did not work and the now there is no light when I flip the switch. The outlet is working fine and I have checked the breaker and it is good too - any ideas? The fixture is only about 4/5 years old,...

I want to convert a half bath into full bath [ 3 Answers ]

Hi, I hope somebody can help! My Mom-in-law is visiting and she has difficulty climbing the stairs. Hence I wanted to convert the half bath at the lower level into a full bath.Any stop gap measure would also work.I really want a low cost solution as we are planning to sell our house in the next...

Adding bath drain in concrete for existing half bath [ 1 Answers ]

I want to turn a half bath into a full bath in my basement. Currently the washer and dryer along with the water heater are in the half bath along with the commode and sink. I want to add a bath tub and the lay out of the room is such that the tub installation would probably require less work if it...

Adding shower to half bath downstairs [ 1 Answers ]

Hello, How would I start the rough in for a shower in a downstairs bathroom if I have a crawl space. Also my plumbing is 1/2 inch pvc and is this large enough for incoming water to the shower. I know you don't have my plans or anything, but all I am looking for is some tips. Also, I just want...

Adding a shower to half bath*rough-in question [ 24 Answers ]

Here's the deal... I am going to be adding a shower to an existing 1/2 bath in my basement. The toilet is vented up out of the slab on the other side of the wall,in my utility closet, makes about a 4' run into another wall where it ties into the lav. /washing machines' drain. the lav./washing...


View more questions Search