    Bathroom circuit
    I am remodeling my bathroom and in the process changing all the electric. Right now the bathroom is fed from a single line connected to a 15 amp circuit breaker. This feeds into a metal junctrion box in the attic. When rwiring is it legal to split that feed into the 3-4 runs I need for the bathroom? I am planing on a vanity light with switch, 1 receptical, 3 recessed lights, and a vent/light. Also I am putting one of the recessed lights over the shower, will anything special need to happen with that?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 25, 2010, 06:05 AM
    Quote Originally Posted by NeedToVent View Post
    This feeds into a metal junctrion box in the attic. When rwiring is it legal to split that feed into the 3-4 runs I need for the bathroom? ?
    Yes, but the junction box will need to be large enough to contain all the wires. There are extension rings/boxes for most types of boxes to add volume to a junction box.


    Quote Originally Posted by NeedToVent View Post
    Also I am putting one of the recessed lights over the shower, will anything special need to hapen with that?
    Check the manufacturers datasheet or instructions, as most will require GFI protection of the fixture if located in a shower.

    Keep in mind that the Code has been for several years that a bathroom requires a 20 amp circuit with #12 wire for the receptacle. This circuit can provide power for the receptacle and any light and fan in that one bathroom only.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Connection of tub to main 3" circuit pipe in bathroom [ 1 Answers ]

I have two questions for reconnecting a 1.5" line from a tub to a 3" line that is part of a circuit wet vent in bathroom (tub, shower, lav and toilet all connected to 1 horizontal 3" line vented at the begining and end by two individual vent lines). 1. what angle should the tub combo/Y fitting...

Concerns with circuit overload because of bathroom remodeling [ 1 Answers ]

I’m in the process of remodeling my basement bathroom and have hit a road-block with the wiring. Here are my questions. • Before I started my basement bathroom remodel, the only thing that was wired in the bathroom was a vanity light from a 15A circuit. This circuit is shared with the upstairs...

Bathroom circuit [ 1 Answers ]

I am putting a new bathroom in basement and want to know the correct wiring. I will be running a 20 amp circuit with a GFI outlet, vanity lighting, and a small exhaust fan. I want to run the fan and lights on their own switches. Can the GFI and others run off same circuit? If so how do I wire...

Bathroom Circuit around corner? [ 2 Answers ]

I am in the middle of a complete remodeling and upgrade of my 80 YO,5' x 9' bathroom. Toilet runs ditect into the 4" vent stack and will remain in the same place. New sink is circuit vented back to the stack and will be moved approx 15" further away from the stack but extending the 2" circuit vent...

Bathroom Vent fan GFCI circuit [ 3 Answers ]

My NuTone fan says that it's UL approved for over shower use when wired with GFCI circuit. Would it be acceptable if I ran the fan power wire first through a plain face (non-outlet, but outlet sized unit) GFCI unit, through the switch and to the fan with nothing else on that circuit? I know that I...


View more questions Search