    Addition of a 220 outlet for welder
    I want to add a 220 V outlet in my garage for a MIG welder. The problem is that I have only 1 space ( 1") left in my electrical panel. All 2 pole breakers that I have seen, with a single trip, take up 2 full spots on the electrical panel. I really dont want to start moving things around in the panel if I dont have to. My question is: Could I use a 20 A tandem breaker that takes only one spot in the panel, and run the 2 hots to it? Furthermore; is there a way I can make this tandem breaker single trip for safety and correctness? Can I buy or make a "tab" if you will, to make this tandem breaker trip together should a problem arise? I thank you in advance for your help. I currently have Cutler Hammer type BR breakers in the panel if that helps.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #2

    Jan 20, 2010, 07:13 PM
    No. The tandem breaker uses only 1 phase of the panel... you will have 120 to neutral from each one, but since they are on the same hot leg of the panel, you would have nothing between them. You may be able to get another tandem breaker and free up another space for a true dbl. pole breaker.
    nick jr's Avatar
    nick jr Posts: 27, Reputation: 1
    New Member
     
    #3

    Jan 21, 2010, 07:46 PM

    Yes but I don't think I was clear

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Change 220 outlet to 120 outlet [ 2 Answers ]

I have removed an old AC unit that ran off 220v and replaced it with a new unit that is 120v. It is #10 wire with black, white and bare copper. It used to be a feed to an old hot tub but when the last AC unit was installed they just used the circuit for that. When installing the new plug can I just...

Switch a 220 v outlet to a 120 v outlet [ 1 Answers ]

I just got an emergency generator and it has a 220 v plug, I will not be using a 220 appliance and would like additional 120 outlets. It seems that I should be able to split the 220 into two 120 outlets. If so how to do it.

Craftsman 220 AC Stick Welder [ 3 Answers ]

Hello Folks, When I purchased this welder I was on my way to installing 220 in the garage. However, those plans fell through and now I need to know how to use the 110 service to Stack the voltages, and provide the same 220 volts to run the welder. I realize the feeds would have to be off...

220 wiring for an arc welder [ 6 Answers ]

I want to hook up a 220v arc welder. I have a 50 amp double pole breaker. The outlet is going to be placed within 6 feet of my breaker box. I believe I have to use 3 wire romex with a bare ground wire. Is this correct? Next, do I connect the black wire to one side of my breaker, the red to the...

220 Welder hookup [ 3 Answers ]

I am installing a 3 prong outlet for my welder, using 8-2 wire. The store gave me 8-3 wire and said to leave one wire out, so witch one do I leave out? I have red,black, white, and a bare ground. Thanks


View more questions Search