    Is it OK to place GFCI on the main and not the sub panel for a spa
    Over the weekend I helped a friend install his spa. The spa had 5 connections and 1 ground. 2 30A, 2 20A, and a neutral. We installed a 50A GFCI to the main electrical panel on the house. Then we ran that to a sub 100A panel with a reg. 20a and 30a breaker in it. Then ran it to the spa. The spa turned on and worked fine. Is it OK that we put the GFCI on the main power board and not on the sub box? I really do not want to get shocked to death in his spa. Thank you
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jan 18, 2010, 06:25 AM
    As long as the spa is GFI protected, does not matter where the GFI CB is located.

    Often the GFI is located at the spa, if it trips it is easier to reset.

    Also helps with the monthly testing of the GFI, if is is conveinently located.

    The other downside of having the GFI at the Main panel is the GFI is now protecting the entire circuit wiring and spa, rather than a short portion of circuit wiring and the spa.

    GFI breakers can sometimes trip for no apparent reason due to long circuit wiring.
    csmith1985's Avatar
    csmith1985 Posts: 3, Reputation: 1
    New Member
     
    #3

    Jan 18, 2010, 11:43 AM

    Yea we were going to use the gfi in the second but couldn't find a 30A gfi. As long as it trips when it is suppose to that's all that we care about. Thank you

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

In a spa installation does the GFI breaker go in the disconnect box or main panel? [ 2 Answers ]

In a spa installation does the GFI breaker go in the disconnect box or main panel?

Wiring a spa GFCI [ 1 Answers ]

Hi, I have a sundance Caprio spa. I have run a 40 amp GFCI breaker from the main panel to the shut off box near the spa. I wired the GFCI breaker by connecting 2 hots, red&black (#8 copper) connecting the white pigtail to the neutral bar in the box and a ground from the ground bar in the main box...

Wiring a Spa GFCI [ 1 Answers ]

Hi, I have a sundance Caprio spa. I have run a 40 amp GFCI breaker from the main panel to the shut off box near the spa. I wired the GFCI breaker by connecting 2 hots, red&black (#8 copper) connecting the white pigtail to the neutral bar in the box and a ground from the ground bar in the main box...

When adding a GFCI disconnect for hottub, should I replace GFCI in service panel? [ 4 Answers ]

I have a hottub now but without a disconnect. Its simply a 6/3-50 amp wire that runs from the hottub to a 50amp GFCI inside the house main service panel. I want to install a disconnect 5-10 feet from the hottub. I bought a disconnect box that already has a GFCI inside of it. Should I have bought...

Gfci spa panel tripping [ 4 Answers ]

I just installed a spa with 4 wires. The house is old and while the neutral & ground bus bars are separate in the spa panel, they are all on the same bar in the main panel. Do I need to install a ground rod by the spa panel to keep the gfci from tripping? (instead of running the ground back to the...