    225 Amp Panel
    I have a 225v main panel and I want to run a sub panel for 13 30amp breakers what size sub panel should I get its for lights that draw 7.5 amps and have 1000w bulbs
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jan 15, 2010, 07:18 PM
    You're not suing 30A breakers for that lighting, are you?? That is a no-no.


    Quote Originally Posted by italy92530 View Post
    its for lights that draw 7.5 amps and have 1000w bulbs
    How many?
    italy92530's Avatar
    italy92530 Posts: 4, Reputation: 1
    New Member
     
    #3

    Jan 15, 2010, 07:45 PM
    There are going to on 3 lights each breaker
    italy92530's Avatar
    italy92530 Posts: 4, Reputation: 1
    New Member
     
    #4

    Jan 15, 2010, 07:47 PM

    40 lights in the room each ballast draws 7.5amps with 1000w bulbs
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Jan 15, 2010, 08:48 PM

    FORTY 1000w lights in one room?? Must be one hell of a room!

    Is this at 120v? Where are you getting 7.5A from.
    1000 watts at 120v is 8.33a not taking into account ballast draws if these are HID lights.

    What are you lighting if I may ask?
    Is this in a residence?
    Is this in the US?

    If this is a residence in the US you CANNOT use 30A circuits.

    This whole thing is very vague. You are leaving out many important details.
    italy92530's Avatar
    italy92530 Posts: 4, Reputation: 1
    New Member
     
    #6

    Jan 15, 2010, 08:57 PM
    It's a commercial building with a 800amp switch gear with a 112kv transformer and I want to run a sub panel for lights in a room that draw(ballasts) 7.5 amps and have 1000w bulbs total of 39 lights the lights are 220v what size sub panel can I put in the room
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Jan 15, 2010, 09:08 PM

    800A at what voltage?
    Is the 112kVA trans 120/240v secondary? (there is NO such thing as "220v" any more)
    Will the panel be wired from the transformer?

    See what I am getting at? WAY too many unknowns.

    PLEASE hire an electrician.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Updating service panel to 200 amp with feeder to 100 amp panel in old house [ 8 Answers ]

I currently in the process of converting 1000 sq ft of attached garage into living space while doing this we are updating electrical service to 200 amp new service, there is 100 amp service in the old part of the house which will remain but need to be sub paneled from the new 200 amp service. I...

200 amp panel feeding a 100 amp panel roughly 130' away [ 7 Answers ]

Hi all, We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away? I want to use aluminum wire as I think copper would be to costly. Thanks for your help in advance, Dude :eek:

100 amp panel to 200 amp panel [ 2 Answers ]

I currently have a home with 100 amp service to a 100 amp breaker box. The box is old and should be replaced, can I have a 200 amp box installed even though I only have 100 amp service?

100 amp sub panel from 200 amp main panel [ 2 Answers ]

We have a 200 amp main panel. We added another floor and decided to add a new sub panel of 100 amps. Is this OK? Should the wire gage be different from 100 maps? Your help is appreciated.

100 amp panel to new 200 amp panel and sub panel [ 3 Answers ]

I have a very small (1000sq feet) 1920 home in Northern New Jersey which 15 years ago was upgraded to breakers with a 100 amp panel. The whole house does have copper romex in it now, and I am adding a substantial addition (3000 sq feet) to the house and I want to put a sub panel in the new portion....


View more questions Search