    johnny cos's Avatar
    johnny cos Posts: 3, Reputation: 1
    New Member
     
    #1

    Nov 16, 2006, 01:42 PM
    Shower drain
    I have a 3" pvc pipe coming out from the concrete. the shower base is already installed and when they put the drain in they just used a 2" drain and put that into the 3" pipe from the concrete. i know the correct way this should have been done was to use a 3" to a 2" reducer. the problem i'm having now is that i'm getting back wash coming up from the drain and since there is a gap from the 3" to the 2" water is running out from underneith the shower base. does anyone know about a 3" to a 2" reducer that can fit into the 3" pipe instead of the outside. Or does anyone know how to fix this without tearing out the shower base. I have already bought a pull tight shower drain that can install from the top of the base so that wouldn't be a problem. Thanks john
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Nov 17, 2006, 05:55 AM
    Hi Johnny,

    I have a hard time believing that a licensed plumber with leave a installation like that. They make a 3 X 2 bushing that's a inside fit but it should be the installers responsibility to make it right not yours. Good luck, Tom
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #3

    Nov 17, 2006, 12:15 PM
    You ask about a 3 x 2 bushing, (see image) check it out at, http://www.horizononline.com/product....phtml/837338#

    Good lucki, Tom
    vpatui's Avatar
    vpatui Posts: 10, Reputation: 0
    New Member
     
    #4

    Nov 17, 2006, 03:54 PM
    Why are you getting backwash coming up out of the drain? Is the shower below grade? Are you sure you have this figured out right?
    johnny cos's Avatar
    johnny cos Posts: 3, Reputation: 1
    New Member
     
    #5

    Nov 17, 2006, 05:37 PM
    I have a water softner and the suds are coming up this is only happening after I wash the soap off. Also this is a basement shower. Thanks
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #6

    Nov 17, 2006, 05:37 PM
    Quote Originally Posted by vpatui
    Why are you getting backwash coming up out of the drain? Is the shower below grade? Are you sure you have this figured out right?
    vpatui,

    I really hate to break bad with another expert but this is the second time in as many posts I've had to step in and correct you. Did you even read the complaint? The plumber left him with a indirect waste. Do you know what a indirect waste is? If you did you would never have posted what you did. And you have the balls to ask him if he figured it out right. He has water coming out of a connection that was left open. How much figuring is there to that?
    I both respect and am grateful for the experts that come on this page that give advice but when I have to step in and correct every post a expert puts out it's time to suggect that perhaps this isn't the category for him. I sure hope you aren't a plumber out in the field running service calls because if you are then you're what gives plumbers a bad name. Sorry vpatui but you're taking up time I could be helping other askers. Sorry, Tom
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #7

    Nov 22, 2006, 04:12 PM
    Hi Tom

    Sorry to email you but I just wanted to let you know that I fixed my shower
    Drain problem in case someone else might have the same problem. My problem was
    That they put in a 2" drain pipe into a 3" pipe coming from the concrete and I
    Was getting backwash coming up from the drain and it was overflowing underneith
    The shower base. First, I bought a pull tight shower drain so it could be
    Tighten from the top of the base. Then I glued 1' of 2" pvc pipe to the shower
    drain. Then I bought two rubber 2" doughnuts and slid them onto the 2" pvc pipe.
    Once I spread some soap inside of the 3" pvc pipe, the 2" pipe with the rubber
    doughnuts on it fix real tight inside of the 3" pipe. I have used this shower 3
    Times and not had any water. Sorry if I took up too much of your time. Just
    Thought this might help someone else. Thanks Johnny Cos

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Installing Basement Shower Drain with Washing Machine Drain [ 5 Answers ]

Hi folks: I would like to install a shower that drains into the same drain as my washing machine. Right now the washing machine drain, 1-1/2" ABS, comes in horizontally about 12" above the concrete floor into a 1-1/2" Tee on a vertical pipe. From this Tee, the vent goes straight up to the...

Shower weep hole drain turned into tub drain [ 1 Answers ]

I am remodeling my shower to a roman tub. The existing drain is a weep hole drain. Is there a plug for these type of drains? The idea is to use the same drain system and hot mop, tile, etc. around it.

Shower leaking (shower drain pipe?) [ 2 Answers ]

Hi, I will apologize up front for my lack of knowledge in plumbing... but I know enough that I believe that I can fix this problem without having to add on the expense of calling a plumber. I noticed that there were a lot of ants coming into our bathroom. After laying traps and having no...

Rebuilding Shower - Leveling new shower drain? [ 5 Answers ]

Hello, I have come to the postings to get some help as I am a novice plumber. I've gutted my ensuite tilled shower down to the floor. In whacking out the cement pan, and I assumed that I've probably cracked the old drain so when I got to the wood floor I cut away the older PVC 2" piping back...

Converting cast iron floor drain to shower drain [ 3 Answers ]

I am adding a bathroom to my basement, which has partial (complete? ) plumbing already roughed into the floor (in 1976). Sewage lift station (vented) is 3 ft from 4" styrofoam plug (toilet), 4 ft from 1 1/2 inch cast male pipe end extending through floor (lav, have already added vertical vent...


View more questions Search