    Gas boiler won't shut off.
    I have a Vaillant gas fired hot water boiler (GA 92 Series). I woke up this morning and the temperature in the house was 8 degrees higher than the thermostat was set at. I figured the problem was the thermostat. I disconnected the thermostat and the boiler still runs. There is only one thermostat and one zone in the house. I looked at the boiler and found where the thermostat wire connects (in the control unit). It is labeled a Honeywell Aquastat Relay (L8148E). I tapped the side of this unit and the boiler went off. I figured something was sticking. I thought it was fixed. The boiler fired up again and will not shut off. Therefore, I turned off the boiler at the breaker box. What to do now?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 7, 2010, 08:46 AM
    Sounds like the control is sticking which means it is defective. Time to replace from the sound of it. Make sure you label ALL wires you remove so they can be put back on the new control in the proper location.

    http://customer.honeywell.com/Techli...0s/60-2278.pdf

    L8148E, great deals on on eBay!
    Thanna00's Avatar
    Thanna00 Posts: 4, Reputation: 1
    New Member
     
    #3

    Jan 7, 2010, 11:34 AM

    Thanks for your opinion. I stopped by the HVAC store and it looks like $200. Is it likely the relay in the control unit? Is it possible to replace just the relay.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 7, 2010, 11:40 AM
    If the relay is plug and play then it would be easy to replace. It should just pull strait out. I believe in some units the relay is replaceable but you have to understand that over the 30 years of that parts production changes have been made so I cannot give you a solid answer but I will look at the diagram and post back.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Jan 7, 2010, 11:45 AM
    It looks like the relay in the current unit is soldered on the board so I guess replacing the relay will not work. If you decide to replace the control GET a tube of the heat conductive compound UNLESS it comes in the box. The control will work much better if you use the compound and the closer control it helps afford will help to keep down the utility costs. READ the above link for the control for more info.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Dunkirk Gas boiler starts up then shut off [ 1 Answers ]

I have a dunkirk Gas boiler. It has been working sporadically lately. Specifically it fires And burners flame on then shut off. I'll turn off power switch and repeat the process And the results are the same. My neighbor came over and bled the system ,removing Sediment that was showing in glass...

How To Shut Off Gas Boiler Wall Vents [ 0 Answers ]

I have an old gas water boiler that uses base board heat. The only name I can see on the units is EASE-RAY. I do not use the upstairs of the house and want to know how to shut the vents up there off. They only thing I can see is a valve that looks like a water valve. Can I just shut them off?

Well- mclain gas boiler main burner shut on and off. [ 1 Answers ]

I have Well-McLain HE boiler with Fenwal control unit. When the termostat start the boiler the igniter lit and after 45 sec the gas start burning and igniter is off, but in around 10 sec it the gas flow stops and in this case there is no lockout. Igniter start lit again and the process continue...

Boiler will not shut off [ 1 Answers ]

I have hot water heating in my home. The boiler will not shut off once it is turned on. I tried replacing the wall thermostat but that did not work. The only way to turn it off is to hit the power supply to the boiler. Any suggestions?

Boiler won't shut off [ 1 Answers ]

I have an old Oil to Gas conversion boiler and for some reason I cannot get the boiler or the circulator pump to shut off. I have a digital thermostat and it is set for 65 degrees but the boiler keeps firing up and the temp in the House is now 72 degrees. The boiler will run for 3 minutes then...


View more questions Search