    Gibson model kg6ra 072c-12a
    Continuous flashing red light, no flames but the blower is working fine. What is the solution to this problem?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 7, 2010, 09:27 AM
    You have low flame sensor signal. Clean the flame sensor with fine sand paper or steel wool. Becareful around the ignitor if you have the new style Honeywell since they are fragile.
    Attached Images
       
    squito's Avatar
    squito Posts: 5, Reputation: 1
    New Member
     
    #3

    Jan 9, 2010, 08:43 AM
    Cleaned the flame sensor and I am still getting the same blinking light and the problem remains the same..
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 9, 2010, 01:50 PM
    Literature

    http://www.nordyne.com/literature/778a.pdf

    See page 30 of this install manual below. I gave you the easiest and cheapest cure as you will find listed on the service blink code section under continuous blink as you described.(false flame/low flame sensor signal)

    Now you are going to get into the gas valve area of the unit. If the wiring is not loose when you wiggle it around and check it for tightness I suggest you contact a HVAC company to make the repair. It is not a simple job since the new valve will need to be installed correctly and adjusted to factory specs using a monometer and other tools of the trade. I also suggest you save a copy of these for your records on the computer. I am sure you will ned these service docs again.

    See page 30

    http://www.nordyne.com/Literature/708291b.pdf

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can circuit work well if we connect 12A load to 20A circuit? [ 5 Answers ]

Hello: I have several equipment which are around 12A. I just can connect them to 20A circuit. But I am not sure if circuit will trip well under overload and short circuit. I know 15A is perfect.But,I don't have 15A circuit Thanks for everybody.

Looking for Gibson SG-X [ 3 Answers ]

Im looking for a gibson sg-x in either yellow or coral. Can't find them anywhere and I really want one

Should W 12a code L amount be deducted from income on 1040NR [ 3 Answers ]

Hi, I have a question about a case of deduction from income in form 1040 NR. There is some amount shown in W2 in cell 12a with code L. This is business expenses reirmbursed. The tax return form is 1040NR for a F1 visa holder. The question is How this amount (with code L) should be dealt...

Gibson dryer [ 1 Answers ]

Dryer started to make a squealing noise then would stop after awhile then it made a bang and the inside doesn't turn but it runs? Was a rubber smell after that? What could this be the dryer is an older 1. Thanks

Gibson refrigerator [ 3 Answers ]

I have a gibson double refridge with the ice maker and water dispenser niether one of them is getting water to them. Anyone have any suggestions on how to fix the problem Thanks in advance:confused: :confused:


View more questions Search