    Bryant 310aav error code 31
    Bryant 310 aav error code 31. My furnace is 3 yr old and gives error code: 31. The blower fan working fine, but the inducer motor does not start. Also the error code tells the pressure switch open not closed.

    Will this be a problem with Inducer motor? What are the various things I need to check to determine faulty inducer motor? How much does it cost to replace the inducer motor?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 7, 2010, 03:39 AM
    Code 31 is a pressure issue. Try disconnecting the small hose and check for any moisture that might come out. Make sure hose is not restricted or cracked.

    You could have a restricted or iced over exhaust pipe that carries the spent gas and byproducts of combustion outside. Check it. You can temporary remove the exhaust from the furnace and see if it runs. If it runs then the exhaust pipe is the problem. NOTE this is for test purposes only just to see if the furnace runs. Reattach after the test or the gas can kill you.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant Plus 80 Error code 33 [ 3 Answers ]

Hello! I'm new on here so bear with me. I found a similuar post on the Bryant 80 but I believe I have a different model... not sure how much that matters. The only model number I could find on the unit was CK5AXA036017AAAA The Error code is 33 Limit or flame roll out switch is open. The furnace...

Bryant furnace error code 31 [ 3 Answers ]

I have a Bryant 350MAV048100 furnace. It runs for 15 minutes, cycles off and then cycles on and shows an error code 31. I've cleaned out the intake /exhaust lines, but still have the problem.

Bryant plus 90i error code 43 [ 1 Answers ]

I have a Bryant Plus 90i furnace flashing error code 43. I'm pretty good at fixing it so far. It's 17 years old and I've replaced the blower and inducer motors. All that seems to be fine. I just check the ususal. New filters are in to give max airflow. Checked and cleaned the condensate trap...

Bryant plus 80 error code 31 [ 1 Answers ]

Bryant Plus 80 furnace - Error code 31 What are the corrective measures to put this furnace back to producing heat? There is power, the fan works but there is no heat. We lost power recently but it worked after that. Last evening there were high winds which were indicated on the code...

Bryant 310AAV code 23 [ 8 Answers ]

I found your forum after having some issues with my furnace. Age is unknown because I rent and my landlords are out of town. When I went to turn the furnace on tonight, nothing happened. House temp registering 68-69 at thermostat, furnace doesn't kick on when adjusted to 72. Fan will turn...