    Comfortmaker gas furnace: LOTS of fan, no flame.
    I have a Comfortmaker gas furnace from 2001. Model N9MP1050B12A1.
    Type FSP. Yesterday morning I noticed the fan didn't stop shortly after the usual heat cycle. I went out to the garage to investigate, & found what I'll call the PVC water outlet line frozen thanks to our new Arctic reality in N.C. Water was spilling out onto the floor from a vertical overflow PVC line up from the point of blockage. Got it unblocked and rerouted away from the low double digit temperatures. No heat since.

    Other observations:
    A: Gas service to the house is OK. Upstairs gas furnace works fine.
    B: Blower fan OK. The only way I can shut it off is at the fuse box.
    C: At the Honeywell SV9541M 2094 module: 4 green lights.
    Found a Honeywell .pdf online for this explanation:
    "Limit string open.Combustion air blower is energized. If control system includes ST9160 Electronic Fan Timer, the heat speed circulating air fan will be energized until the limit string resets."
    With advice to Check/Repair:
    1. Open manual reset or auto reset burner rollout switch.
    2. Open high temperature or auxiliary limit switch.
    3. Limit and rollout switch wiring in good condition and securely connected.


    I'd like to narrow down the causes & in effect, the solutions based on what I've provided. I suspect the water overflow is at the crux of the problem. As I had no issues prior. I'll need some advice on what the questionable component looks like, as HVAC is not my strong suit.

    Comments? Advice? Suspicions?

    Thanks for reading.

    -John
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 4, 2010, 09:42 AM
    Kill power.
    Recycle power back on. It it works great if not then

    Kill power. With a ohm meter or other testing device track down all limits and other control that might have failed then reset if possible and reactivate unit.

    Naturally follow the advice give you by the machines blink/flash codes and check them also.

    Link to part locations and wiring diagrams.

    http://icpindexing.mqgroup.com/docum...4003101003.pdf

    One last tip. It is possible that other furnace components froze so Apply some heat (electric box heater etc) to the front of the furnace while the drain line is watched to see if more water flows.
    AVLMCO's Avatar
    AVLMCO Posts: 3, Reputation: 1
    New Member
     
    #3

    Jan 4, 2010, 11:21 AM

    Thanks to your input I have heat! I reset the 3 rollout switches after proving there was no leftover ice in the line. Let me do something nice for you someday. THANK YOU! -John
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 4, 2010, 11:24 AM
    Glad you got it going.
    Attached Images
     
    AVLMCO's Avatar
    AVLMCO Posts: 3, Reputation: 1
    New Member
     
    #5

    Jan 4, 2010, 11:34 AM

    YOU fixed it. I was just a guy following instructions. Going to go turn it down now. Getting a little warm in here. :-)
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Jan 4, 2010, 01:06 PM
    Yes but you actually did the fixing. I just hang around here giving pointers in the right direction.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Blower Fan on gas Comfortmaker RPG Heat Exchanger runs intermittently [ 3 Answers ]

Hello, I'm new here, and I've been reading a lot (well, 4 or 5 pages anyway) of what's already been asked, and I haven't found my specific problem... yet. This gas hot air furnace was installed circa 1987? So, Here's what's happening. (I actually timed these cycles with a second-hand.) Turn...

Furnace blower will not stop after flame goes out on gas furnace [ 1 Answers ]

Furnace blower will not stop after flame goes out on a gas furnace

Comfortmaker RPJ II (2) gas furnace short cycling during idle [ 13 Answers ]

I have a Comfortmaker RPJ II (Enviro plus 90) gas furnace connected to a programmable thermostat that works and cycles on and off fine when inside temp is lower than set target temp - exhaust blower cuts on, pressure switch engages, igniter glows, valve opens, pilot lights, valve opens, jets...

Comfortmaker gas furnace will not ignite. [ 3 Answers ]

My furnace was working yesterday and we did not turn it off, but it will not function today. I know there is electrical power at the unit; that there is gas supply; the filter is new; the inducer motor comes on when the thermostat is adjusted;but no flame appears. The inducer motor will remain...

Comfortmaker Furnace Fan blows in line fuse and will not allow furnace to work [ 1 Answers ]

I have a Comfortmaker Furnace (approximately 1998/99) and the fan will not turn on allow the furnace to heat. When I try to turn the furnace on it blows a 3 amp fuse at the blower motor. I removed the fuse and jumped it and all it will do is make a faint buzzing noise and not turn on. I can...


View more questions Search