    Troubleshooting rheem furnace
    I turn the forced warm air rheem gas fired furnace on at the thermostadt from off to hest and the furnace goes through its cycle and starts. It runs for 5-10 minutes and provides heat and then shuts off and does not restart itself automatically/ I can turn it to off and to het on the thermostdat and it will restart again. It has a vent pipe instead of a flue and it is windy and cold on the outside where the furnace vent pipe is located. Any thoughts?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Jan 3, 2010, 07:10 PM

    Check vent pipe outside to see if its frozen shut(or restricted at all). Do you see any lights blinking in through the covers of the furnace when furnace is not working?
    tony603's Avatar
    tony603 Posts: 1, Reputation: 1
    New Member
     
    #3

    Mar 3, 2012, 06:46 PM
    My furnace turn on for a few min and the turn off but the fan continues to run and blow cold air
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #4

    Mar 3, 2012, 07:34 PM
    You should have a flashing code on the control board that you can read looking through the small window on the lower blower door. Count the blinks of the light and it will give you the fault code. Are your return air filters clean?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Troubleshooting rheem water heaters [ 8 Answers ]

I have a Rheem 50 gallon electric water heater model 81VR52DT. Setup with Therm-o-Disc thermostats double element non-simultaneous operation. Problem is that lately we are running out of hot water. Both top and bottom elements have 20ohms +/- resistance (measured with a Fluke 8060a). The bottom...

Rheem furnace troubleshooting [ 3 Answers ]

My Rheem quit lighting. I cleaned flame sensor nothing. It does work once in awhile. The 2 green leds light no orange. Once in awhile when it lites I get steady orange. When it tries to lite it will go through whole sequence lite for 10 seconds then go out. Then it won't work for several days. I...

Rheem furnace light troubleshooting [ 5 Answers ]

I have a Rheem Criterion II gas furnace. Unit starts and runs okay most of the time. However it will stop firing up occasionally and will go into 1 hour lockout mode. In an hour it will fire up or when you open unit which automatically reset it. It will them fire up okay. What is causing unit to...

Rheem criterion ii troubleshooting [ 22 Answers ]

I have a Rheem Criterion II gas furnace, that quit working. I checked it out, and found that the ignighter would come on, the gas would start, and then it would shut off. Figured it was the flame sensor. Before I could sand or replace it, it quit even doing that. I didn't get voltage off the...

Rheem Troubleshooting Codes [ 1 Answers ]

I need to know the Rheem Troubleshooting codes on a RGPH-12EAR JR. Or if you could tell me how to get the mannual for this, that would be great.


View more questions Search