    Furnace blower motor
    My furnace blower motor will run properly on "Auto" but will not operate at all on "On".
    What's going on?

    Thanks,
    trazmo
    trazmo's Avatar
    trazmo Posts: 6, Reputation: 1
    New Member
     
    #2

    Dec 31, 2009, 11:16 AM

    I forgot to mention, I have replaced the thermostat (Honeywell electronic).

    Trazmo
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Dec 31, 2009, 12:02 PM
    Time for you to revist your thermostat install. The G terminal is what controls the manual operstion of the blower. If not the wiring then check the thermostat setup program to be sure all your settings are correct.
    trazmo's Avatar
    trazmo Posts: 6, Reputation: 1
    New Member
     
    #4

    Dec 31, 2009, 12:31 PM

    Thanks for the input. Done what you suggest, all is correct. I was having the problem before the new thermo, that's what prompted me to install it.
    Any other thoughts?
    Thanks,
    Traz
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Dec 31, 2009, 12:53 PM
    If it is working correctly at this point the job is done since I am sure you caulked or plugged the area where the thermostat wire comes through the wall on the back side of the thermostat. This prevents inner wall drafts from creating problems with the thermostat temperature sensing device.
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #6

    Dec 31, 2009, 01:27 PM

    What type of furnace? Model?
    trazmo's Avatar
    trazmo Posts: 6, Reputation: 1
    New Member
     
    #7

    Dec 31, 2009, 02:53 PM

    Comfortmaker
    GUH100A016CIN
    parttime's Avatar
    parttime Posts: 1,440, Reputation: 113
    Ultra Member
     
    #8

    Jan 1, 2010, 08:04 AM

    trazmo, are you sure of the model #? Can't seem to find anything using that number. I think HVAC1000 (he's the expert) thinks your problem is solved, you might need to repost. Good luck
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Jan 1, 2010, 08:43 AM
    I just picked back up on this. I misread the post and thought the problem was over. Usually the furnace blowers ON thermostat selection is controlled by a relay. On newer furnaces this relay is located on the circuit board but older units have a stand alone relay. I have located your furnace BUT I have no wiring diagram for it. Does you furnace have a circuit board?
    trazmo's Avatar
    trazmo Posts: 6, Reputation: 1
    New Member
     
    #10

    Jan 1, 2010, 08:54 PM

    Yes, it has a circuit board
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #11

    Jan 2, 2010, 06:42 AM
    Usually the circuit board contains the blower relay. See if there is 24 volts from the thermostat green wire to ground. This is at the G terminal in the unit. The G terminal is what activates the blower when using the ON selection at the thermostat.
    trazmo's Avatar
    trazmo Posts: 6, Reputation: 1
    New Member
     
    #12

    Jan 3, 2010, 08:32 PM

    I checked out the board and a lead was burnt out. I reapaired it an now motor run normally in both the "on" and "auto" positions. Thanks for the suggestions they led me in the right direction.
    Over and out,
    trazmo
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #13

    Jan 3, 2010, 08:47 PM
    Glad you got it running.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace blower motor [ 10 Answers ]

I have a Climatrol Furnace, and it stopped working. I called a Heating Co, and the technician said that that the motor was bad, it's and old unit with Climatrol no longer in business. I might be able to find a used motor, but I really need a new furnace. After he left I was reaching in and I was...

Furnace Blower Motor Runs Constantly & Furnace or AC Won't Run [ 2 Answers ]

I have an Armstrong forced air (induced draft) natural gas furnace with central AC (made around 1990 -- Model: EG6H80DC14-1, Serial: A18315MNA). I had a problem at the end of the heating season where the blower motor would run continuously (even when the thermostat is turned to "off"). I thought...

Furnace blower motor [ 2 Answers ]

I need a blower motor for a 20 year old Bryant +90. Motor Model: HC43SB1100. Having trouble finding this. Is this the numbers I need or do I need the furnace numbers? Thanks, Al

Goodman furnace will ?heat motor? And blower motor will run but not at same time [ 2 Answers ]

I have a 2 year old Goodman, gas, no heat pump. There is a flashing LED that blinks once ever 4 seconds. Also, blower motor does not stay on always. We did smell something like an electrical burn. I'm guess my blower motor is fried?

Furnace Blower motor [ 10 Answers ]

Should the furnace blower motor fan be set to auto or on? Which is best for the home? For the motor?


View more questions Search