    Wiring two 230 Volt pool pumps inseries
    Hello,
    I am rewiring switched for two pool pumps. The old set disintegrated so I cannot tell how they were wired. The two pumps are recirc and booster and are both 230v. I would like to wire them so that the booster can only turn on when the first pump is on. How can I manage that wiring with no loss of voltage?
    johnmprince's Avatar
    johnmprince Posts: 56, Reputation: 4
    Junior Member
     
    #2

    Dec 30, 2009, 02:29 PM

    Add a contactor to the recirc pump circuit to close when the recirc pump is on. Wire the contacts of the contactor into the circuit of the booster pump. This way if the recirc pump is not on the booster pump cannot come on.
    raking08's Avatar
    raking08 Posts: 2, Reputation: 1
    New Member
     
    #3

    Dec 30, 2009, 02:38 PM

    Thanks! So there is no way to do this simply based on wiring the 2 30 amp dbl pole switches?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Dec 30, 2009, 04:22 PM

    What turns on the pumps? A switch? A breaker? Where is it located? What is the HP rating of the pumps?

    The problems are protecting both motors separately and having them both turn on together.

    I am thinking on the lines of a NEMA class enclosure for wet environments and two DIN rail breakers and a watertight switch on the outside of the enclosure. You would need two contactors to do this. One for each motor.

    Motor starters would be a better choice to protect the motors. You have to look at replacement costs and wheter it's worth it. I would get a case large enough to put in two DIN rail motor starters.

    DIN rail is basically an erector set for controls.
    johnmprince's Avatar
    johnmprince Posts: 56, Reputation: 4
    Junior Member
     
    #5

    Dec 31, 2009, 01:12 PM

    Kiss's points are well taken. If the controls are in a potentially wet area use the proper enclosure. Most of these pumps are thermally protected. They have a thermostat right in the motor housing to protect it from overload. They generally have some sort of strainer to keep big stuff out of the impeller so stalls are not a big concern. Watertight enclosures are expensive, if you can keep the controls in a dry place you are better off. The motors should be on separate circuits if possible. They are not wired in series at all.
    Another way to do this is to use a three pole switch for the circ pump, using the third pole to make a break one leg of the boost pump. Then use a double pole switch, one leg through the circ pump switch, to feed the boost pump. In this case these pumps should be on one circuit. It is most likely a code violation to have feeds from two different circuits in the three pole switch. If KISS knows for sure let me know.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #6

    Dec 31, 2009, 03:33 PM

    Switching one leg won't work if this is a disconnect.

    Good point about the internal thermals, very good motor protection.

    I guess the one issue is that there is a disconnect nearby. Plugs can serve as one and so can a disconnect. Nice thing about disconnects as that they are lockable off.

    As long as the system is protected by a GFCI and metal is properly grounded to the pull pump and a LOCAL disconnect is available and the power requirements are OK then you should be able to:
    1. put pump controls in a water tight encloseure (see Lowes/Home Depot)
    2. You need a HP rated switch and/or contactor (waterproof is tough to achieve)
    3. Two contactors rated for the motors is easy to achieve.
    4. 230 V coils is easy to achieve
    5. A watertight On/off switch is easy to achieve with two independent contact blocks.
    6. DIN rail construction is easy to achieve
    7. You could make one pumps power switch the other contactor.
    8. You could make it current sensor based, then if the first pump failed, the other would turn off.
    9. You could put DIN rail mount breakers sized for the motors.
    10. You could use motor starters instead of breakers.

    You MUST:
    1. ground properly
    2. Have a local disconnect means (can be plugs).
    3. Be protected by a GFCI
    4. Have a properly sized supply(s).

    We really can't help much further without motor sizes (FLA/HP) and service size to the pool and what's currently in place.

    I read your post again and saw "Can be turned on If the other pump is on"

    Is it CAN? MUST? One or two switches? Where are they now?

    You can also post pictures using "Go advanced/Manage attachments"
    \\

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I operate 230 volt machinery with 480/277 volt [ 7 Answers ]

480/277 volt 3 phase power is the proposed electrical service for a for a new building. Will I be able to power machinery that requires 230 volt 3 phase?

Wiring instructions for 240 volt pool pump timer [ 4 Answers ]

Can you supply wiring diagram for a 240 volt timer for swimming pool pump. The wire from the pump (240 volt) one black, one white and one green. I assume both the black and whit are load and should be connected to the two load terminals on the timer. Is this correct?

115/230 volt wiring [ 11 Answers ]

I bought a beautiful chandelier at a garage sale at a great price. Can the chandelier be wired for 230 volts for use in the Philippines as long as 230 volt bubs are used?

230 volt Motor wiring [ 11 Answers ]

I have a 6 hp 230 volt air compressor motor that I have wired on a twin 20 amp breaker with a 10/2 wire. I cannot get the motor to start, I have took it off and had it checked and it works fine, just not when I wire it up in my garage. I do have power at my 10/2 wire, and cannot understand why it...


View more questions Search