    Troubleshooting Trane gas furnace.
    T-State is calling, vent fan is running, blower fan is running, have gas and valves open.. . But ignitor doesn't glow.. . Checked voltage to it and have less than 12V.. . What next?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #2

    Dec 29, 2009, 04:31 PM

    Check all limits(high limits and rollout switches). Only the vent fan should run when there is first a call for heat. IF both vent fan and blower are running, it leads me to believe you have a limit problem.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #3

    Dec 29, 2009, 04:47 PM
    Status light blinking?
    Attached Images
     
    fmkaspick's Avatar
    fmkaspick Posts: 3, Reputation: 1
    New Member
     
    #4

    Dec 30, 2009, 07:38 AM

    As a matter of fact, yes, I did have an error code - 3 flashes - Vent Pressure Switch Error. However, I thought I cleared that when I got the vent fan running by helping it start by turning the blades with a screwdriver.. . Though it's still flashing. This furnace hasn't run since last winter.
    zanec's Avatar
    zanec Posts: 26, Reputation: 3
    New Member
     
    #5

    Dec 30, 2009, 09:00 AM

    If this is an XE 90 unit, I've had problems with the pressure switch and the tube coming from the plenum to the switch collecting condensation which will clog it. I'm not an expert but maybe check the hose and the switch, also the little nipple on the pressure switch itself might be clogged. It worked for me.
    fmkaspick's Avatar
    fmkaspick Posts: 3, Reputation: 1
    New Member
     
    #6

    Dec 30, 2009, 01:39 PM

    I haven't check that yet even though I do recall reading re just such a problem in another post. I'll report the results after I check it.
    zanec's Avatar
    zanec Posts: 26, Reputation: 3
    New Member
     
    #7

    Dec 30, 2009, 03:20 PM

    Ok. Another thing that is most likely the problem: if you manually had to help the fan to start, the motor could be bad or the capacitor could be bad. Sometimes the capacitor will visibly show signs of it being bad like fluid coming out of it or it could be shaped like a soda can that was left in the freezer. The problem code is correct. It's not closing the pressure switch because the fan isn't running in it's sequence time. The fact is, you shouldn't have to help the fan motor start.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Troubleshooting guide on a trane xe-80 furnace [ 9 Answers ]

I have a trane xe-80 furnace, And there is a code that flashes Thermal code protection. We have cleaned the heat sensors is there anythig else I can do to get heat till the Holiday weekend is over?/

Do trane gas Furnace have belt and how to fix trane gas Furnace [ 1 Answers ]

I have trane gas Furnace and its stopped working the pilot is not working its keep shutting off and also the switch on and off is working but the pilot and burner is not working what should I do ?:(

Trane XL 80 Gas Furnace [ 1 Answers ]

I have a Trane XL 80 Gas Furnace that is not working properly. The LED trouble light flashes twice repeatedly. The burners will not light but blower runs just fine. I can turn off the breaker for a few minutes (while I am checking everything else out) and turn it back on and everything starts...

Trane Gas Furnace [ 3 Answers ]

The Gas furnace is running however there is no heat coming out from the furnace directly and the blower is not coming on. The heat is set to 68 however it is 64. There is no blockage in the vents. Why is this happening. We just had an ice storm but it seems like whenever it gets very cold outside...


View more questions Search