    I grounded the outdoor power service box, do I need to ground my main panel as well?
    If I do, then what gauge of wire should I use for grounding my main panel?

    Is there any difference if I connect the ground to sewage pine or water pine?

    Thanks.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Dec 19, 2009, 11:13 AM

    Details. We need details.

    First, where are you? US? (State?) CA? UK?

    What specifically is an "outdoor power service box"? And why did you "ground" it? And to what?

    In the US:
    Sewage pipes are NOT suitable for use as an electrode, nor are they required to be bonded.
    A metallic water pipe that is in contact with the earth for 10' or more must be used as an electrode and must be supplemented by another electrode.

    There are quite a few important codes involved with doing a service. Did you get to know them before you started?
    pubema's Avatar
    pubema Posts: 9, Reputation: 2
    New Member
     
    #3

    Dec 19, 2009, 12:40 PM

    I live in Illinois. The power meter box outside of my property is grounded with 1/2in thick and 5ft long copper rod into the ground.

    The question is: Should I still ground my main panel?

    Thanks.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Dec 19, 2009, 02:49 PM

    I'm not sure about Ill, but most places in the country now prohibit a grounding electrode connection inside the meter pan.

    Also, a 1/2" x 5' rod is NOT code complaint and WILL get red tagged. You need and 8' x 5/8" ground rod.

    YES, you need to run the grounding electrode conductors and any bonding conductors to the main panel/disconnect.

    Where did you get your information from before starting this project?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Ground/Neutral Bus in Main Service Panel - Is there a Difference? [ 8 Answers ]

I'm preparing to provide new wiring to a sizable addition to a log home. Prior to beginning the new work I mapped my existing circuits thinking it best to correct any potential overloads in the existing panel/circuit design before introducing any new problems on my own. Decided to make a few...

Adding a bus to a main panel for ground. [ 2 Answers ]

I have recently added on a room to my house. I have a main power supply out side with a two pole 100 amp breaker the neutral and ground are on same bus, the ground continues down tocopper pole in ground. Upstream ihave added alager box to accommodate more poles. The new box has the two hot wires...

How much is a main panel box? [ 10 Answers ]

I need to replace my main panel box and the electrician that came out said he would charge $1400.00 for a new box and to install it. Is that a fair price because a few months ago another quoted me a price for the box of $350.00. Also what size of panel box does it take for a 1200 square foot...

Using a old main panel as a junction box [ 1 Answers ]

I'm working on a burn out house, it has a 200amp service on it, the owner has added so many new things to the home including a 3 story addition, that I'm having to upgrade to a 400 amp service. The inspector said it had to be a side by side set up, the existing 200 amp service is in such a...

Outdoor electrical circuit 400' from main meter box [ 3 Answers ]

I want to add two circiuts to a junction box , apx 400' from a pass through electrical box on my property, I had put in underground 1 1/4 cunduit with a pull box every 100 feet when the house was built. What size cable should be used for this, it will need to handle 2- 20 amp circuits


View more questions Search