        Wiring electric baseboard heating
       
                  
        I have calcuated the watts needed for a room to be 2000 watts to heat an addition.  I have 240 volt base board heaters.  I have double pole thermostats.  I am using 12/2 wire.  Now my question is... the wiring in the heaters are red/black on the right side and black/black/red on the left side. 
 Could someone tell me how to properly wire this in layman's terms..  I know it is difficult to explain, but the directions are borderline worthless.
 
 I am using a double pole 20 amp breaker... right?
 
 When I get to the last heater, I don't need to do anything do I?  Like run a circuit or anything like that?
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Printers & Electronics Expert |  | 
 
                  
                      Dec 15, 2009, 07:18 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        You are working backwards.  Check the metal label on the baseboard heaters to get the correct voltage (240 does sound correct).  More importantly, you need to get the amperage rating for the heaters.
 
 Once you know that, then you can size the wire.  12/3 supports up to 20 amps.  If your heater requires more than 20 amps then you need change both the breaker (20 amp) and the wire (12/3 also 20 amp)
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Junior Member |  | 
 
                  
                      Dec 15, 2009, 07:33 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        OK... I need to get 12/3 wire... it is 240 volt.  I have read that you can have up to 4000 watts or 16 feet of heater hooked up to one breaker.  Could you walk me through the process of hooking it up though..  from the breaker to the thermostat to the heater..  the wiring inside the heater is different than what I am used to.
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Uber Member |  | 
 
                  
                      Dec 15, 2009, 07:38 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        I'm confused too with this statement  
	
		
			
			
				
					  Originally Posted by OP the wiring in the heaters are red/black on the right side and black/black/red on the left side. So, your going to have to help out here.
 
OK, the rest says 
Take the total wattage of the heaters: I = 2000/240 
Multiply I by 1.25 = I = 1 * 1.25
 
Move the size to next higher available breaker size: 15 or 20 A; Use that breaker size
 
If it's 15 A; 14 or 12 AWG is permissible 
If it 20 A; you must use 12 AWG
 
I'll let you do the math
 
In general in wiring the wire goes from the breaker to the first heater, to the thermostat and then to heater #1 and then to heater #2 and then to heater #n.
 
The thermostat must be able to handle the first I:  2000/240
     |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Junior Member |  | 
 
                  
                      Dec 15, 2009, 08:52 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        OK... there are places for wiring on either side of the heater.  One side has 2 black wires wirenutted together.  One of the blacks goes directly into the heater.  The other goes into a black cylinder that also has a red wire attatched to it which then goes into the heating element.  The other side has a red and a black wire wire nutted together, the red gos into the black cylinder that leads into the element and the black goes into the heater.
 
 Why do manufacturers waste paper and ink on directions..  just a simple how to wire would be great... instead, they clutter the directions and make them too vague.
 
 I know it is a pain, but I need laymans directions to installing.  Start from the double pole 20 amp breaker.  I have already figured out the amperage and the load is perfect for the 20 amp breaker... so I have 3 base board heaters-1 thermostat-12/3 wiring... then I...
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Printers & Electronics Expert |  | 
 
                  
                      Dec 15, 2009, 08:58 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        If you are using a straight 240 VAC connection and the amperage is less than 20 amps, then you really only need 12/2.  You use 12/3 if you you were going to need 120/240 VAC.
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Uber Member |  | 
 
                  
                      Dec 15, 2009, 09:27 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        OK, lets assume that the black cylinder is an temperature safety.  This is in series with the heating eement.  Thus I'm guessing you have a free red and black wire.  There should also be a way to attach to ground.
 
 Lets use 3 conductor wire with ground to make things easier to understand.  We can change to to conductor later.
 
 At the panel red and black attach to the two pole breaker, ground(bare) is connected to the ground bar, white is capped off.
 
 IF USING 2 CONDUCTOR WIRE, (BLACK/WHITE), YOU TAKE SOME RED ELECTRICAL TAPE AND TAPE THE END OF THE WHITE WIRE RED)
 
 Back to having a red/black/ground
 
 The thermostat should have two wires labeled LINE and LOAD.  LINE comes from the breaker box and LOAD heads to the heater.  Lets assume 2 red and 2 black wires.
 
 The RED LINE terminal goes to the breaker.  The BLACK LINE termonal goes to the breaker.  The RED LOAD termonal goes to the RED termonal of the 1st heater.  The BLACK LOAD terminal goes to the BLACK terminal of heater #1
 
 Now take the Blacks from the heater #1 and connect to the wire heading to heater #2.  Do the same for the whites.
 
 IF there is a heater #2, connect from heater #1 as above.
 
 So when you look at the imaginary picture, there 4 wirenuts with two wirenuts on them at the stat.
 
 Three black wires wirenutted  together at the 1st heater and three reds wirenutted at the 1st heater.
 
 The last heater has two reds and two blacks respectively, wired together at the last heater.
 
 If you had three heaters, yes it's possible to branch to either side from the middle heater.  That just means more wires together at the middle heater which can potentially be harder to deal with.
 
 Grounds should ALWAYS go to the device first if there is a terminal and your using a metal box.
 
 If the tstat is in plastic box, then just put the grounds together.
 
 The heater probably has a small green pigtail, so all the bares get connected there.
 
 -----
 
 Aside:
 
 Assume you were wiring a duplex outlet in a metal box.   You'd connect the white, black and bare directly to the outlet.
 
 With a purchased green pigtail with a screw and an fork terminal, you'd connect the fork to the duplex outlet and the other end with a scre to the grounding screw in the bottom of the box.
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Uber Member |  | 
 
                  
                      Dec 15, 2009, 12:06 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Re-labeling:
 
 If it wasn't clear, it always makes sense to re-lable or recode wires used for different purposes.  Green isn't allowed to be re-coded.
 
 One use where this should happen is when wiring a 120 V switch where a 2 conductor wire (black/white) is run from the ceiling to the switch.  Since it switches the black wire, the white is re-coded at both ends with a bit of black electrical tape to be a black wire.
 
 Similarly, if white is a hot wire on a 240 circuit, it should be re-coded with red tape.
 
 Now you know what all those pretty colors are for:D
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Junior Member |  | 
 
                  
                      Dec 15, 2009, 03:07 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Great... thanks..
 
 The thermostat says that the black is the load and the line is the red.  The diagram also indicates that the 2 blacks go to the heater and the 2 reds go to the panel.  So just to clarify.  I am wiring the 2 reds to the panel, then I am wiring the 2 blacks to the first heater.  I am running a 2nd line from the first heater to the second heater and then again from the second heater to the third.  The third heater is the last heater.  Now there is no more wiring after the third heater... right..
 |  
    |  |  
	
		
	
	
  | 
    
      
              |  | Uber Member |  | 
 
                  
                      Dec 15, 2009, 03:25 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Sounds good!
 |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Jan 16, 2011, 12:28 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Why are there three wires coming out of a baseboard heater wall thermostat 220v
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | Electrical & Lighting Expert |  | 
 
                  
                      Jan 16, 2011, 01:22 PM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        
	
		
			
			
				
					  Originally Posted by redmeadows   why are there three wires coming out of a baseboard heater wall thermostat 220v Are you asking the original poster? I think this is long done after over a year.
     |  
    |  |  
	
		
	
	
  | 
    
      
                |  | New Member |  | 
 
                  
                      Dec 9, 2011, 09:14 AM
                  
                 |  |  
  
    | 
        
        
        
       
                  
        Multiple Baseboard heaters must be connected in parallel in order to work properly!
     |  
    |  |  
 
 
 
  
    | Question Tools | Search this Question |  
    |  |  |  
 Add your answer here.
 
Check out some similar questions!
Electric baseboard wiring woes
 [ 7 Answers ]
I am  perplexed. 
 
I have a 240v line feeding a brand new Marley baseboard heater.  It has an integrated T1 style thermostat. I used 12/2 w/gr. ROMEX per Code.  Fed from a Cutler Hammer panel, 20 amp twin breaker. 
 
I have the Blk solid hot Line connected to the Blk stranded wire to the Tstat. 
...
 
Thermal relay kit wiring to electric baseboard
 [ 3 Answers ]
On the baseboard heater are to wires line 1   and line 2  , I connected the main power supply to these wires but my thermal relay kit now has to be wired to this,  I have a yellow, blue and black wire  and  white and brown wire that connects to a low voltage thermostat. 
 
 
How do  I connect all...
 
Baseboard Heating - Panel Wiring
 [ 4 Answers ]
I wired my 220V electric baseboard heaters on to Cutler Hammer 20 Amp Double Pole breakers but now they don't work.  The panel is all double pole breakers but the original baseboard heater wiring was staggered, so each hot wire was on a different double pole breaker. 
 
I now have each hot wire...
 View more  questions
Search
 
 |