    Wiring 125/250 V receptacle
    The previous owner of this house disconnected the three prong 125/250 V receptacle from the wires before he left. My dryer has a 3 prong cord and matches the receptacle. I need to rewire the receptacle. The wall box has 4 wires. Red, black, white and bare copper. Which wires go to the receptacle and which one is not needed and stays unattached to anything in the wall box after I hook up the receptacle. I suspect the bare metal ground is not needed here but want to be sure. Also does it matter to which terminals I attach the remaining three wires. I suspect I attach the red and black to the w similar appearing contacts and the white to the dissimilar contact. Please help thanks. Jonathan
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #2

    Dec 14, 2009, 02:03 PM
    The most recent edition of the NEC (Electrical code) requires 4-prong range and dryer receptacles in all new installations, so this is a great opportunity to bring your receptacle up to code.

    Buy a four prong receptacle and a new 4-prong cord for your dryer. It should be intuitively obvious how to wire it up, but ask the hardware store guy if you aren't sure.

    Another important thing is to remove the "bonding screw" that connects the neutral wire to the frame of the dryer. (This screw was required for a 3-prong plug, but must be removed when you install the 4-prong plug)
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #3

    Dec 14, 2009, 02:05 PM

    Well a three prong recep. Would not be rated 125/250. Just wouldn't.

    Usually the round pin is ground. It should be connected to the screw on the outlet first and also bonded to the box if metal.
    The other two would be brass in color and they can be connected to Red or white.

    White or neutral should be capped off. You should make sure this is attached to the neutral or usually the ground/neutral bus in the main panel.

    Can give more help if needed.

    PS: Agree with the above post. Change to 4 prong.
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #4

    Dec 14, 2009, 02:33 PM
    [QUOTE=KeepItSimpleStupid;2130138]Well a three prong recep. Would not be rated 125/250. Just wouldn't.

    Old dryer and range receptacles were 3-prong, and were rated 125/250. The neutral was bonded at the appliance, and served as a ground.

    According to most sources, this was written into the code during WW2 in order to save a small bit of copper. (this may be an urban legend, someone needs to check old NEC's for when this was first allowed)
    In the 1990's, this was finally corrected, and all new construction requires the ground and neutral to be separated.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Dec 14, 2009, 02:44 PM
    Quote Originally Posted by KeepItSimpleStupid View Post
    Well a three prong recep. would not be rated 125/250. Just wouldn't.

    Usually the round pin is ground. It should be connected to the screw on the outlet first and also bonded to the box if metal.
    The other two would be brass in color and they can be connected to Red or white.

    White or neutral should be capped off. You should make sure this is attached to the neutral or usually the ground/neutral bus in the main panel.
    Sorry KISS, I know Bob corrected this but I really feel the need to clear it up a bit.

    Older range and dryer receptacles were "non-grounding" 125/250v with two hots and a neutral. The advice to cap off the neutral is quite dangerous. The neutral is required in these older circuits. It was the ground wire that was allowed to be omitted.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #6

    Dec 14, 2009, 03:37 PM

    Thanks.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #7

    Dec 14, 2009, 03:52 PM
    I can't believe someone actually said "ask the hardware store guy". Aren't hardware stores where the "guy" wires up a cord with two male ends for Xmas decorations?. sheesh

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring a receptacle to a three wire and two switches [ 9 Answers ]

Hello, I have two switches, three wire coming into the box is red black and white. Switch 1 is connected to the red and is connected to the other switch 2 with a small white wire. Switch 2 is connected to the white wire coming in and the black wire. I want to install a receptacle that runs all...

Circuit Breaker/Wiring/Receptacle Ratings [ 3 Answers ]

If you run from a 20 amp breaker with 12/2 wire each receptacle rating has to be 20 amps? 20amp breaker-------->with 12/2 wire------->to 5 outlets In other words if you go to the store to buy the receptacles they can't say on them 15A max because the breaker it is run from is a 20 amp right?...

Wiring a switched receptacle [ 1 Answers ]

I would like to run my pool filter and chlorine generator off the same switched receptacle. My pool filter has a plug which I would like to keep so I can store it over the winter. My chlorine generator is hard wired to it's own circuit. I would like to install a switched receptacle to run my...

Wiring GFI receptacle [ 2 Answers ]

Trying to wire a GFI receptacle at my kitchen sink. Receptacle in double gang box with a light switch. Original wiring consisted of two white wires to side of original receptacle. Two black wires to each terminal on the switch for a light over sink and a black jumper from switch to the...

Receptacle wiring [ 3 Answers ]

I want to add a receptacle to a box I have in my pantry that has an existing light switch. I have a three wire load coming in to the box from the circuit breaker. The red is wired to the switch and the blacks and whites are connected with wire nuts. The three wires feed other boxes in my kitchen....


View more questions Search