    How do I wire a thermostat for a wood burning furnace?
    I have a wood burning furnace that feeds into a natural gas furnace. I'd like to add a second thermostat near the one for my gas furnace. I'd like to wire it in such a way that it turns on the blower motor in the main furnace when the house gets cool, but I want to set the main thermostat lower than the wood burner thermostat in case the wood fire gets low and the gas burner will kick in. I just don't know how thermostats are wired.
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #2

    Nov 24, 2009, 04:12 PM

    Wow. If I understand your post correctly you are asking for something that is a bit beyond simple thermostat wiring. If you don't know how to wire a basic thermostat to your wood stove, I think it may be a bit beyond you to do a thermostat, relay and probably transformer just with help from here. A decent HVAC tech won't have any trouble, but I've even seen them do some convoluted solutions to non-standard setups like this.

    Actually, as I was typing that last sentence I realized that it could be done really neatly with one 2-stage thermostat and (if required) relay isolation for the wood stove. Still won't be exactly simple. I don't have the time to do a wiring diagram drawing for you, and I would need some information that is missing in your post to really be certain I would be hooking things up correctly. Maybe one of the list professionals could help farther.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Nov 24, 2009, 07:36 PM
    This is all I have for this
    Attached Images
  1. File Type: pdf AD%20ON%20FURNACE%20BLOWER%20WIRING.pdf (50.3 KB, 758 views)
  2. woodmizer101's Avatar
    woodmizer101 Posts: 2, Reputation: 1
    New Member
     
    #4

    Nov 30, 2009, 02:53 PM

    Did you get an answer on this? I am doing the same set up. I have learned several things. I tried wiring a second thormostat across the pwr and fan terminals. From red to green thinking the original thermostat would remain un changed but this caused a problem. When the auto/on switch is in Auto and you power up the fan the AC will also come on. I moved the switch to ON, removed the green wire from main thermostat and ran it to a second thermostat. Powering the second thermostat also with a wire from the R of the first thermo. This works fine for now but is not the best set up. I believe I may be able to makes things better by adding a swich at the furnace and break the wire to the AC and having a summer / winter selector I would move twice a year. Let me know if you solved this problem already.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    Nov 30, 2009, 06:50 PM

    Piece of cake.

    To make it simple, set up the wood burning thermostat for conventional heat. You can also connect C to C if present.

    Jumper Rc to Rh if present and we'll call these terminals R.

    Connect R of the wood t-stat to R of the furnace t-stat.
    Connect W of the wood tstat to G of the of the furnace t-stat.

    This would say if the wood stove called for heat, the fan would come on. It also says that the fan will run continuously when the wood stove was out.

    The way to fix that is to put a NO thermal switch on the flue of the wood stove and interrupt the connection to the other thermostat.

    This way, the flue temp, would determine if the fan stays on.

    For the initial lighting of the wood stove, until the stove got hot enough and if you wanted to have the blower running during that time just use the G switch on the thermostat.

    Another way, would be to use a time delay relay and a push button wired at the stove. This would engage the fan for x time and you'd push it when lighting.

    Sorry, don't know enough about wood stoves to know if the fan nees to be running during lighting or not.
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #6

    Nov 30, 2009, 08:06 PM

    As I said earlier, use a two stage thermostat. You would hook the gas furnace up as the second stage of heat (W2) and then set the second stage differential to 10 deg or thereabouts. Nothing would be hooked up to the first stage terminals (W1). Set the thermostat to call for heat at 80 degrees (10 degrees or 2nd stage differential above where you want the gas to kick in) and the fan will be on as long as the temperature is below the first stage set temp. The gas furnace will kick in at 70 degrees and you will have it all done in one thermostat.

    If you need W1 to call your wood stove somehow, you would have to isolate it with a relay. A 2 stage heat pump thermostat would work fine, as they often don't have a W1 terminal to worry about. Just make certain the one you use has an adjustable 2nd stage differential and shuts the second stage off when it is satisfied, not when both stages are satisfied.

    If you need wiring help I will need to know more specifics on your existing thermostat and the exact requirements of both heat systems.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #7

    Nov 30, 2009, 08:23 PM

    Some tstat manufacturers (Honeywell, for example) won't tell you how there tstats work.

    EP:
    Can you suggest a possible tstat? Link to a manual?
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #8

    Nov 30, 2009, 08:43 PM
    Quote Originally Posted by KeepItSimpleStupid View Post
    Some tstat manufacturers (Honeywell, for example) won't tell you how there tstats work.

    EP:
    Can you suggest a possible tstat? Link to a manual?
    I actually think the higher units in the FocusPro line will do what I suggest. Honeywell's website is lousy for getting help quickly, so I am not going to look that up now. ClimateMaster has a unit that would do it, models in the ATP32U series. I think some of the ICM multi-stage tstats might. The 2210 would work and it's cheap. If you need more than 6 deg for the differential setting you would have to use W3 with that one. I use the ICMs because we need max temperature lockouts. They are not a high end unit, but as I said, they're not pricey. White-Rogers and RobertShaw have units but I can't come up with numbers quickly.

    Just some ideas. Google them, the mfgr links come up early.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #9

    Nov 30, 2009, 09:27 PM

    Furnace Filters, Air Conditioner Filters, Air Quality - iaqsource makes it easy to get info. It's organized very well for what they sell.

    It's hard getting info as to whether a thermostat say drops W1 when a W2 call happens. I suppose it does. But try to find that in writing.

    I looked here: http://www.ntsupply.com/files/products/9915i.pdf

    For specs on the Robert Shaw 9915i stat and all I have is questions. Like what is the max differential? The table says O & B terminals. Does it mean it has both? There's probably another manual somewhere.
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #10

    Dec 1, 2009, 05:17 PM
    Quote Originally Posted by KeepItSimpleStupid View Post
    <snip>It's hard getting info as to whether a thermostat say drops W1 when a W2 call happens. I suppose it does. But try to find that in writing.

    I looked here: http://www.ntsupply.com/files/products/9915i.pdf

    for specs on the Robert Shaw 9915i stat and all I have is questions. Like what is the max differential? The table says O & B terminals. Does it mean it has both? There's probably another manual somewhere.
    I only use manufacturers websites for information. Most mfgrs have installation manuals for their tstats and those are where you will find how to set them up correctly. Honeywell has very good information, but their search function is absolutely pathetic. Don't search for a complete part number! And keep everything you find on your computer so you don't have to go through the agony again.

    I don't believe that I've ever seen a fossil fuel tstat that drops W1 when a higher number call comes in, they are called in addition (see next paragraph for exception). The functionality that I suggested for the OP required that when W2 (or W3) is satisfied, they will drop out and leave the earlier calls in. Of course if there is any stage not satisfied, the fan will be on, which I believe is what he wants.

    A heat pump tstat may disable the compressor (1st stage heat) on a call for emergency heat. Depends on how it is configured, but even that will still have the fan called.

    That RobertShaw that you mentioned is a NICE tstat. Expensive too. And yes, they don't give you the max differential in the manual. I think you got the sell sheet. Here is the manual from the manufacturer. http://www.icca.invensys.com/manuals...w/110-1069.pdf I have one on my parts shelf if you really need to know that information.

    I wish the OP would come back and give more detail on his requirements. If he wants the fan to be on all the time the woodstove is hot, and when it is cold, then the fan will run only when the fossil fuel furnace is called, then my idea won't work well. He will need two tstats for that the scenario, the one to call the fan for the woodstove would have to be set for cooling, and then he probably would need relay isolation for the two. The question was vague enough that I almost didn't jump in. Now I have spent a lot of bandwidth just about thermostats.

    EPM
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #11

    Dec 1, 2009, 05:28 PM
    If it was me I would keep them separate. Had the same situation here years ago with a wood fired boiler and a separate thermostat makes troubleshooting later when a problem comes up a lot easier. This type of a situation can also be helped along with a add a wire type device so no more thermostat wires need to be brought to the thermostat location.

    FAST-STAT

    Or if you are really cheap just use a simple non digital thermostat along side the fast stat that is installed with a isloation relay in the furnace.
    landon0861's Avatar
    landon0861 Posts: 1, Reputation: 1
    New Member
     
    #12

    Dec 31, 2009, 02:13 PM
    Try a basic bimetallic thermostat that requires no power, place it near the wood stove to register heat and splice your nat gas call wire to it, when it senses heat from wood the call wire circuit will be open and only your fan should run. When the fire goes out the circuit will re-close and the system will operate normally. You may need to play with the settings on the thermostat or the distance or location of the thermostat. This might cost you about $40 if you buy a new t stat

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wood burning stove blower thermostat [ 1 Answers ]

I bought a new blower fan for my buck wood burning stove insert and the thermostat that used to have 3 speeds high, med & low now only works on high. I figure I hooked the wires up wrong when I got the new blower fan. Any suggestions on the wiring? Eric

How to wire a blower&thermostat on a franks heat wood/coal furnace [ 1 Answers ]

I have wood burner in my garage that all the wiring has been dismantled.I recently installed a new blower and I want to wire it to my thermostat which is a honeywell with 4 wires yel,wh,bla, & gr. It also has an automatic damper. There is an existing transformer. Can someone please help me

Wood burning furnace [ 1 Answers ]

I have a wood burning furnace that has a problem burning out the motor because of sand. I there a sealed blower motor that can be put on a Harman 100 wood pellet burning furnace? I am told by the contractor that there is no such thing

Wiring thermostat to wood burning stove [ 1 Answers ]

Thank You Mike, What I did was just hooked up a squirrel cage with a motor to the wood burner. Now I want to make it run off a thermostat. Just have the two wires coming off the motor.


View more questions Search