    240 2 pole with 120 split off
    Folks-

    I am building a special project box and can't figure out why my breaker keeps tripping...


    I have a 240v 2 pole GFI breaker 30 amps supplying power to the box via 4 wire 10/3 feed. Inside the box, on the back side of the outlet power comes in on, I'm tapped/bridged off one of the hots and the neutral and take it over to a small computer device (also within the box, which is about 12" square and 8" deep). The other hot goes through a relay, and then to a heating element (which is NOT hooked up for testing).

    The computer only pulls about 1amp, so I'm sure that's not it. For testing, I disconnected everything from the feed and wired a 40 watt desk lamp in, and as soon as I turn it on that side of the breaker trips.

    Arff? How come? And can this be rectified? (no pun intended)
    Tev's Avatar
    Tev Posts: 232, Reputation: 20
    Full Member
     
    #2

    Nov 18, 2009, 03:44 PM

    Is the neutral wired to the 240V GFCI breaker like it should be or directly to the neutral bar? If your breaker does not have a place to wire the neutral then the breaker will not work for this application. To wire your GFCI properly take the neutral to the proper lug on GFCI and the pigtail on the GFCI to the neutral bar.

    A straight 240V GFCI compares the current on each of the two hot legs and trips if they are not the same. A 120/240V GFCI also measures neutral current and figures it in.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Advantages of a 480/277 3 phase Volt system over a 120/240 [ 2 Answers ]

I have customer that needs to upgrade his service from 800Amps to 1200Amps. He currently has a 120/240V 3 phase system and a 120/240V System With 2 separate Meters. I am advising that he upgrade and go to a 1200Amp 480V 3 phase system and transform down for existing loads. Will he save any costs on...

Wiring in a 240 volt single pole thermosat in wall heater [ 3 Answers ]

I have installed a new wall heater and it came with a single pole thermosat, after I had it all wired I cannot get it to shut off regardless of which way you turn the stat.

Double pole or single pole thermostat for baseboard heater [ 2 Answers ]

A more specific question here: My 240v baseboard heater says it can be wired with a single or double pole thermostat. Since 240v is already "dual pole" with two hots, do I want to stick with a double pole thermostat? Are there advantages/disadvantages to each? Thanks.

One pole of untied double-pole circuit breaker breaks [ 5 Answers ]

I recently purchased a new dryer (220 v appliance) to replace an older model. The old dryer was connected to the panel via a double-pole breaker except that there was no clip or tie between the poles. I changed the location of the outlet when installing the new dryer, replacing the cable with the...


View more questions Search