    Lennox 51M33 stat to Hunter 44860 stat
    Lennox Heat Pump with Electric heat backup
    Lennox 51M33 wiring
    O - orange
    R - red
    G - green
    Y1 - yellow
    W1 / E jumper - white
    L - light red (pink)
    C - black
    T (Outdoor temp sensor) - blue

    Hunter 44860
    C - black
    Y1 - yellow
    RC/R - red with no jumper
    W2 / E jumper - white
    O- orange
    G - green
    L - pink
    Blue wire not currently connected

    My questions are, do I need to reconnect the jumper on RH-RC/R and where if any do I need to connect the blue wire since it was connected to the "T" slot
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Nov 11, 2009, 04:30 PM
    Jumper - yes. Insulate pink and blue wires as they are not needed.
    Mcgyver's Avatar
    Mcgyver Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 11, 2009, 06:04 PM
    KC,

    Thank you for the reply, The jumper has been reconnected and the pink and blue have been disconnected.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #4

    Nov 12, 2009, 04:04 AM
    Success?
    Mcgyver's Avatar
    Mcgyver Posts: 3, Reputation: 1
    New Member
     
    #5

    Nov 12, 2009, 07:13 AM
    I hope so, the furnace was working and the inside temperature was nearly at the setting 68*, outside temp was 30* Thanks again and I will give more info as I gather it.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Old lennox with standing pilot and cam stat cycling [ 8 Answers ]

Hi gents Old lennox model 9803-980-2 H.boy 68000 BTU with a honeywell fan limit cycling every 5minutes . The wires disconnected at the Stat and jumpered . Still the furnace acting same problem . The motor and blower wheel and pilot acting quite normal . Do you think the fan limit is faulty...

Hunter t-stat wiring-44660 [ 1 Answers ]

5 wires yellow green blue white red,connections G,Rc,Rc1,Rh,Y/O,W/B,Y1 what wire goes where?

Replaced lennox t-90 t-stat w/ hunter just right -still not fixed [ 1 Answers ]

Original problem was my blower was kicking on for about 10 seconds without the furnace lighting up and sending heat with the blower then it would cut off about 10-20 minutes later the furnace and blower would run its normal heating. Changed the lennox for a hunter just right digital and had some...

Just 3 wire T-Stat connection, new stat, diff letters [ 6 Answers ]

Hi all, I've done tons of reading and can't find my specific wiring, tstat combo to figure it out... hopefully someone can shed some light on it for me. Natural gas forced air furnace, no air conditioning. Had a honeywell for the last 9 years, easy install, labelled easy. (but its dead) Wire...


View more questions Search