    Furnace shuts off
    HI,
    I have a furnace that won't stay in. The blower keeps blowing, but the heat cuts out because the flames get shut off every two minutes or so.

    Over the summer, we remodeled and streamlined the duct work. We eliminated lots of big runs that absorbed all the heat. Now, though, I think we do not have enough. We have one small duct run blowing directly into an open auditorium (its for a church. We don't keep the heat on constantly, but instead need to be able to heat the room quickly when the building is used. Could the problem be from this--not enough returns or vents?

    Secondly, I'm not sure if the gas is open all the way. We shut it off this summer, and there is an old valve. The flow through the lines is weak. Someone said that is how gas lines are supposed to be. Someone else said it should have more pressure. Would that cause it to keep turning off the heat?

    The unit did survive a flood. Don't know if that could have blown something either. Thanks for your help
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #2

    Nov 4, 2009, 05:32 PM
    Sounds like you have a collection of problems. The short-cycling may be due to overheating, typically the result of inadequate airflow. The high-limit control will sense over-temp conditions and interrupt heating until things cool down a bit. The gas pressure issue should be investigated. Typically, natural gas inlet pressure should be maintained between 5"-14" W.C. under full operating conditions. A static test of gas pressure won't reveal problems that may occur under demand. Additionally, I'm sure the "bath" didn't help.
    letmetellu's Avatar
    letmetellu Posts: 3,151, Reputation: 317
    Ultra Member
     
    #3

    Nov 4, 2009, 09:01 PM

    If you are heating a large room like a Church and the inside air is very cool it is possible that the fan switch is cutting itself off because of the cool air being pulled into the return air grill. If you know how you can reset the fan stitch to a Higher OFF setting and also raise the differintial between the on and off. This will make the Air coming out of the furnace hotter and maybe heat the Church faster.
    jerrygallow's Avatar
    jerrygallow Posts: 3, Reputation: 1
    New Member
     
    #4

    Nov 4, 2009, 10:14 PM

    Thanks for the responses. I noticed tonight that it is blinking four times, which says "open main limit/ aux limit" on our furnace. I guess that probably means there is not enough ducting?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #5

    Nov 5, 2009, 02:21 AM
    Based on your description of the situation, that is likely the case. You mentioned "streamlining" the duct system. Can you be more specific?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace ignites but blower won't start till furnace shuts down. [ 7 Answers ]

(Nordyne/Miller G3RA)-I have a furnace HSI(glow plug) that will ignite and burn until it gets too hot and shuts down. As soon as the furnace shuts down the blower starts to circulate air. The blower circulating air cools the furnace and it reignites.Shortly after the furnace ignites the blower...

Furnace shuts off gas [ 1 Answers ]

My furnace randomly lights both sides. After the igniter comes on, the gas kicks in on the igniter side but not on the temp. probe side. It seems that the gas doesn't flow over to that side after it comes on. Is it a blocked valve or gas jet?

Furnace shuts off and on [ 1 Answers ]

Furnace lites, runs for about 30 secs-1 min then shuts off then re-lits and does the same thing over and over. Furnace has pilot control module, what could be the cause

Furnace not heating the house. Damper on the furnace not opening. Motor then shuts. [ 4 Answers ]

My forced-air furnace is not working correctly. The gas works heating the air in the furnace, but When the motor starts the damper doesn't open and the Motor shut down. I need suggestions?:mad:

Furnace shuts off [ 2 Answers ]

My oil furnace will shut off during the day or evening. I can usually get it going again by pressing the restart button. Even then, sometimes it won't click in, sometimes it will run for half a minute and shut down. If I restart a few times with very short runs, it evventually will run for an hour...


View more questions Search