    Service Size
    Is a 100 amp service on a 640 square foot house with electric baseboard heating adaquate?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Nov 2, 2009, 03:26 PM

    Sounds Like enough. Can you list all Appliances, Gas Dryer? Kiln, Welder, Dock, Jacuzzi, InstaHeat(Demand Water Heater)
    rustydog's Avatar
    rustydog Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 2, 2009, 04:57 PM
    There is an electric dryer stove and hot water tank
    rustydog's Avatar
    rustydog Posts: 3, Reputation: 1
    New Member
     
    #4

    Nov 2, 2009, 04:59 PM
    Quote Originally Posted by Stratmando View Post
    Sounds Like enough. Can you list all Appliances, Gas Dryer? Kiln, Welder, Dock, Jacuzzi, InstaHeat(Demand Water Heater)
    There is an electric stove dryer and hot water tank
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Nov 2, 2009, 06:04 PM
    How much heat? New construction would dictate around 4,000 -5,000 watts.
    eriknugent's Avatar
    eriknugent Posts: 90, Reputation: -5
    Junior Member
     
    #6

    Nov 2, 2009, 08:21 PM

    Your calculating out to about 65.5 amps without the heat if stan I right that pushes you up to 86.3 amp if I where you I would go with a 150A give you some room to expand and your not talking that much of an increase in price.
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #7

    Nov 2, 2009, 08:27 PM
    Doing as much of a standard calculation as info gives:

    General Lighting Load: 640 sq. ft x 3VA/sq.ft=1920 VA
    2 kitchen Circuits= 3000 VA
    laundry Circuit=1500 VA

    Total: 6420 VA

    1st 3KVA @ 100%----------3000VA
    Remainder at 35%---------1197 VA==========3197 VA
    Dryer----------------------------------------------------5000 VA
    Range----------------------------------------------------8000 VA?
    Water Heater--------------------------------------------5000 VA?
    Baseboard Heat-----------------------------------------4000 VA?

    Total VA-------------------------------------------------25197 VA

    25197VA/240 Volts=105 amps

    Standard Calculation put you over. If you are allowed to compute the Optional Method, (Check with your local inspector) Using the same information:

    General Lighting load: 1920 VA
    Kitchen and Laundry: 4500 VA
    Dryer------------------5000VA
    Range-----------------8000VA?
    Water Heater------- 5000 VA?
    Baseboard Heat------4000 VA?

    Total VA---------------28420 VA

    First 10,000 VA @ 100%----------10,000 VA
    Remainder at 40%----------------7296 VA

    Total VA... 17296 VA
    17296 VA/240 Volts===========72 amps


    Still cutting it close! Not much room for expansion there. Have you considered gas heat, hot water and range?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Nov 3, 2009, 03:04 PM
    Need to correct a few errors in this calculation, and added some clarity, my corrections in red:

    Quote Originally Posted by ohb0b View Post
    Doing as much of a standard calculation as info gives:

    General Lighting Load: 640 sq. ft x 3VA/sq.ft= 1920 VA
    2 kitchen Circuits= 3000 VA
    1 Laundry Circuit= 1500 VA
    Total: 6420 VA

    1st 3KVA @ 100%----3000 VA
    Remainder at 35%----1197 VA
    Subtotal................. 4197 VA
    Dryer----------------5000 VA
    Range---------------8000 VA Allowed Load for one range in dwelling
    Water Heater--------4500 VA Typical Load for typical WH
    Baseboard Heat------4000 VA? As good a guess as anyone, thou should be higher

    Total VA------------25697 VA

    25697VA/240 Volts = 107 amps

    Standard Calculation put you over.

    If you are allowed to compute the Optional Method, (Check with your local inspector)

    Per code, the designer is allowed to use the optional methods, rarely does an inspector have any say in this, as the designer is the responsible party in sizing the service.


    Using the same information:

    General Lighting load: 1920 VA
    Kitchen and Laundry: 4500 VA
    Dryer------------------5000 VA
    Range-----------------8000 VA
    Water Heater----------4500 VA
    Baseboard Heat------ 4000 VA?

    Total VA--------------27920 VA

    First 10,000 VA @ 100%--10,000 VA
    Remainder,17920 at 40%---7168 VA

    Total VA.........................17168 VA
    17168 VA/240 Volts======72 amps


    Still cutting it close! Not much room for expansion there. Have you considered gas heat, hot water and range?
    Sorry OH, but there was a math/typo error in the beginning of the calcs, but with me changing the size WH load, still brought the results close.

    A 100 amp service, based on the little information given, and assumptions on the heat KW, is sized adequately.

    This is why I dislike doing these calcs, as the info needed is critical.
    ohb0b's Avatar
    ohb0b Posts: 215, Reputation: 14
    Full Member
     
    #9

    Nov 3, 2009, 03:19 PM
    Sorry for the typo and math error. I thought I double checked it.. but remember I added 3000 and 1197 in my head, instead of using a calculator!

    Yeah, I don't know anyone who has ever used the standard calculation. I just assumed there might have been a local requirement in some jurisdictions to use it.

    Personally, I put everything I can on natural gas.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable size for 100 amp and 200 amp service. [ 16 Answers ]

I would like to know what size aluminum sec I would need for 100 or 200 amp service

Service Size [ 1 Answers ]

Hello, My question is this: Let's assume you see #6 gauge copper wires entering a service box with 60 A fuses, then #3 copper wires going from the fuses to the 100 A breaker in a new combination panel. That is all that is provided, or that you can see. What is the service size? Please help...

What size service? [ 13 Answers ]

My wife and I are building a new house. We more than likely will go with in floor electric radiant heat. And we'll more than likely go with a multiuse tankless water heater or point of use electric water heaters. We figure that since we'll go with electric radiant, we don't see the point in getting...

Size of service [ 1 Answers ]

Hi my name is will we just built a 24x30 garage detached I already have conduit running from the house to the garage. My question is what size wire do I need to run to the garage? What size service do I need I plan on having 4 or 5 florecent lights garage door opener, 10 outlets, a mig welder...

WHAT WOULD BE The best size AWG to use for an 80 and 100 amp service [ 2 Answers ]

This in reference to a regular size commercial run


View more questions Search