    NYC water pressure
    I would like to know if there is a minimum requirement for water pressure supplied to an apartment in a high rise in Manhattan.
    If so, where can I find written documentation.
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Oct 31, 2009, 05:26 AM
    Quote Originally Posted by microllins View Post
    I would like to know if there is a minimum requirement for water pressure supplied to an apartment in a high rise in Manhattan.
    If so, where can I find written documentation.
    What's your PSI in your apartment? This can be checked by a hose bib gage,(see image) attached to a washer hose faqucet. What floor do you live on?
    Did you ever have good pressure? Most high raises have booster pump installed about midway up the building. Where's yours? Let me know, Tom
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #3

    Oct 31, 2009, 11:08 AM

    I do not think there is any requirements as per say. . Average pressure in the US is around 35 psi. I know areas here in So.California that have only 20 psi and then you go 30 miles away and pressure is 180 psi.

    Highrises present different problem. Water is usually pumped in to a storage tank located up on the roof. Water then falls down by gravity. I worked in the City (Mid-Town and Upper East Side ) for several years and the biggest problem were deteriorating and undersized pipes. Also, sometimes real estate speculators convert regular buildings into condos to maximize their profist. They do nice remodel - but forget about upgrading plumbing system.

    What you have is most-likely inadequate volume delivery, not pressure.

    What are the symptoms ? Please, let us know, so we can advice. Thanks. Milo
    microllins's Avatar
    microllins Posts: 13, Reputation: 1
    New Member
     
    #4

    Nov 1, 2009, 09:24 AM

    It's actually an apt that we did a renovation in. the new showerbody has a thermostatic pressure balance and conforms with the new restricted flow parameters. And if I remember correctly, the flushometer is a 1.6 flush.
    The pressure at the riser is 17 psi +-.
    The problem is, prior to our work, her delivery was fine using the old gate valves in the shower and the 3.5 flush.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #5

    Nov 1, 2009, 09:38 AM

    Your remodel did not change your pressure but you may have caused a restriction that reduces your volume. What type and size valves did you use?
    microllins's Avatar
    microllins Posts: 13, Reputation: 1
    New Member
     
    #6

    Nov 1, 2009, 09:56 AM
    Quote Originally Posted by ballengerb1 View Post
    Your remodel did not change your pressure but you may have caused a restriction that reduces your volume. What type and size valves did you use?
    We used ball valves at the riser. The branch was 3/4 to the flushometer and 1/2 to the lavatory and shower. Everything was replaced exactly as it was originally.
    I did locate a chart in the NYC plumbing code stating that 25 psi is required at a temp controlled showerbody, and 20 at this type of flushometer valve.
    I think the pressure/flow has always been inadequate, but the original equipment allowed unrestricted flow so it wasn't apparent.
    Milo Dolezal's Avatar
    Milo Dolezal Posts: 7,192, Reputation: 523
    Plumbing Expert
     
    #7

    Nov 1, 2009, 12:13 PM

    Truth is that new valves are made with restricted water flow. Also, your shower head has flow restrictor in it. Did you try to remove it and run water w/o the flow restrictor ? Also, some high-end temp-valves, like Hansgrohe, Grohe, Dornbracht, Jade, Axor, KWC, etc. have filter screens inside that may be partially restricted by debris from remodel.
    microllins's Avatar
    microllins Posts: 13, Reputation: 1
    New Member
     
    #8

    Nov 1, 2009, 12:50 PM
    Quote Originally Posted by Milo Dolezal View Post
    Truth is that new valves are made with restricted water flow. Also, your shower head has flow restrictor in it. Did you try to remove it and run water w/o the flow restrictor ? Also, some high-end temp-valves, like Hansgrohe, Grohe, Dornbracht, Jade, Axor, KWC, etc. have filter screens inside that may be partially restricted by debris from remodel.
    I've removed and tested pressure at the shower head, the shower body and the flush valve. There was a bit of flux in the screens. But after cleaning the difference was minor. I changed the diaphragm in the flush valve to a 3.5 and it got much better.
    We tested the pressure at the main feed in the basement, calculated the drop due to rise to the 1th floor, and we're getting what we should. So there doesn't appear to be any supplemental booster in line.
    I guess my bottom line is, we need to use the restricted flow devices to meet current code. So if there were a minimum psi requirement to residential apartments that is not being met, we could focus on resolving that issue.
    I've been doing renovation work in Manhattan for the last 7 years, there is always a noticeable drop with the new fixtures. I'm nearly at the point of reinstalling unrestricted flow devices and ignoring the code requirements.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New hot water heater installed, but no hot water pressure. Plenty of cold water? [ 11 Answers ]

Hi, I own a small plumbing service and have a problem I've never encountered before. I installed a new top vented gas water heater for a customer. Turned the main back on, bled air out of the lines, etc. Problem is there is no hot water pressure throughout the house. Cold water pressure is fine....

Cold water pressure is lower than Hotwater pressure [ 1 Answers ]

In the bathroom sink, I see the hotwater pressure is very good . When I open the cold water it is very low. It is was fine 2 weeks ago. What could be the problem? Thanks Asaad

Low water pressure causing high blood pressure [ 1 Answers ]

I have low or no hot water pressure to the downstairs bathroom. I've replaced the cartridges, valves and hot water heater, still no pressure... help.


View more questions Search