New Member
|
|
Oct 29, 2009, 06:01 PM
|
|
Bryant spark ignitor
This Bryant furnace stumped me. It sparks, pilot comes on and burners come on for about 20 seconds and goes off. I have changed the Flame sensor in front of pilot flame.
The Flame sensor has a white wire going to a Spark Power pack, and the red wire goes to the spark rod.
I get the same result after changing the Power Pack which also has 3 wires coming from gas valve. SOMETHING is shutting the gas valve down after 20 seconds.
I do know that on some other brands of furnaces that the Spark Rod also acts as a flame sensor. There's no model numbers left to be read other than the first 3 number "394".
I also changed the control board, and with all that... I still get the same results.
WHAT CAN IT BE?
|
|
 |
Ultra Member
|
|
Oct 29, 2009, 06:48 PM
|
|
I'm not for sure but I thought the 394 model was a standing pilot furnace. Can you send a pic of the furnace so we can see what you have?
|
|
 |
New Member
|
|
Oct 29, 2009, 06:54 PM
|
|
I wish I could T-Top, but it was at a residence's place and it stumped me. The Bryant model starting with "394" is not a standing pilot. It has a double blower fans inside. You might say it's a fair size.
There's a THS, MV and a ground wire coming from gas valve to Power pack plus the sensor wire and the red spark wire.
|
|
 |
Ultra Member
|
|
Oct 29, 2009, 07:07 PM
|
|
To me it sound like it has a re-lite kit added to the system. If the flame sensor is grounded touching a burner or rust around the bottom it will do this, or if the spark ignition control is not properly grounded same symptom.
|
|
 |
New Member
|
|
Oct 29, 2009, 07:19 PM
|
|
I replaced all new and nothing is touching anything... believe me, I racked my brain on this one and I have been doing this for 12 years. The only thing I can now come up with is that maybe a bad gas valve.
|
|
 |
Heating & Air Conditioning Expert
|
|
Oct 29, 2009, 08:56 PM
|
|
Hook your meter up to the gas valve terminals. Fire over the unit. When the flame drops out see if voltage is still being supplied to the gas valve. If voltage is still being supplied to the gas valve then you know the valve is bad.
Now if this unit has a 2 or especially a 3 wire pilot then the pilot warp switch is subject to be junk or someone might have replaced the glow coil setup with a spark setup. If the pilot has 3 wires suspect it. Unplug 3 wire pilot and jump yellow and green wire not on the pilot but the wires going back to the controls. This should keep it on constantly and if it is the 3 wire pilot then this test will tell you if it is bad or not.
Note do not try to adjust the safety pilot to make it work. That can turn into real bad news if it is not adjusted perfectly.
Note sometimes you can hit the pilot area with a screwdriver and the unit will start working again. This was always the quick test but unpluging and testing with a jumper is always best.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Bryant 383KAV Furnace - Code 14 - Not getting 120 volts to ignitor
[ 4 Answers ]
Still scratching my head on this one. Everything appears to be working fine on my furnace, except that the ignitor is not getting juice to glow orange/white, hence the gas is not igniting? I disconnected the ignitor harness from the control board, ran the test sequence again, and determined that I...
383KAV Bryant Furnace - Code 14 Not getting 120 volts to ignitor
[ 1 Answers ]
Still scratching my head on this one. Everything appears to be working fine on my furnace, except that the ignitor is not getting juice to glow orange/white, hence the gas is not igniting? I disconnected the ignitor harness from the control board, ran the test sequence again, and determined that I...
91' civic std, no spark, new ignitor
[ 1 Answers ]
91' civic, cranks great but doesn't start. Followed some suggestions found here & thought my igniter was bad. Replaced... still no start ( I'm not the best with a multimeter). Any other suggestions. Have been trying to follow TXGREASEMONKEY. Sounds like definitely a genious.
Noise in spark ignitor box
[ 2 Answers ]
After replacing a gas valve in my carrier furnace with spark ignitor the service tech told me I was having pressure problems with the gas service line. He showed me that the pressure would drop down to 0 and then back up to to operating pressure. I had the gas company come out and they replaced...
View more questions
Search
|