    Fan turns on but burners don't ignite and doesn't blow either hot or cold
    :confused:We can hear the fan turn on and the thermostat is much lower then what heat is turned to. It usually kicks on, but it does nothing. The fan runs for a little while and then just turns off and no air is blown either hot or cold. There is no pilot light on our unit, it's an electronic ignition.
    There is a red light on the circuit board that blinks 3 times pauses and then blinks again.
    Please help
    myers's Avatar
    myers Posts: 3, Reputation: 1
    New Member
     
    #2

    Oct 28, 2009, 09:47 PM

    Our furnace is a Goodman and is 2 years old. The fan was making a screeching noise earlier today and now we don't have any heat.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Oct 28, 2009, 09:54 PM
    If it was making that kind of noise I would suspect a bad fan motor. Being only two years old it is probably under warranty for the part. Contact the company you bought it from.
    myers's Avatar
    myers Posts: 3, Reputation: 1
    New Member
     
    #4

    Oct 28, 2009, 10:08 PM

    Thanks, in the door the 3 blinking lights indicate "Pressure switch stuck open" would that have anything to do with the fan motor?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Oct 29, 2009, 02:10 AM
    The pressure switch is not closing but stuck open. The inducer fan could cause this.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Rhemm Burners won't ignite! [ 5 Answers ]

Hello, I have a Rheem Criterion II about 15 years old. Down Draft Furnace I just replaced the blower motor and it works great. The problem is when I fire up the furnace the blower comes on the ignite r glows and than just when the burners should ignite the system stops? The green lights on the...

Gas burners on furnace do not ignite [ 3 Answers ]

The gas burners on my furnace do not ignite. When I turn on the heat at the thermostat and set the temperature to a setting higher than the room temperature I can hear a faint click within a couple of seconds. Within a few more seconds the blower comes on, but the burners never fire up. There is a...

Burners will not ignite [ 1 Answers ]

I have a Day/Night forced air heater and the burners will not light. The fan runs but the igniter glow device does not turn red and the gas valve does not open. I have run the on test mode and the igniter glows red but when turned on by the thermostat the igniter does not work. I have checked the...

Gas furnace burners won't ignite [ 4 Answers ]

17 year old gas furnace... burners won't ignite. What are the logical troubleshooting steps to solve this problem?

Burners won't ignite--no gas? [ 1 Answers ]

Lennox model GMP075-3. Installed in '95. I've tried resetting according to instructions on access cover panel (turn heat to 'off', turn off power to furnace, turn gas valve to 'off' for 5 minutes, etc.) When I call for heat, small (induction?) fan runs for a few seconds, the igniter unit glows...


View more questions Search